OpenSCADA
Documents/How to/Create module
This manual is primarily made to help in building the modules for OpenSCADA. The module creation may be required at wish to add the support for new data source or other extension to OpenSCADA. Since OpenSCADA is an extremely modular system, all interfaces of interaction with the external environment are implemented by expanding it with modules of following types:
But since the transport interfaces implemented by the modules allow communication with various devices on them, this document is expanded with a short instruction with links on creating internal Functions, DAQ-Templates, UI-Widgets, as well as designing Libraries with them for placement and publication in the official OpenSCADA library collection.
1 Creating a new Module
In order to post the developed module to the OpenSCADA source tree repository, you must do the following and comply with the following requirements:
Modules in OpenSCADA are the shared libraries, which are dynamically connected to the OpenSCADA core at startup or during the program operation. Many of the modules can be disabled, connected and updated during the operation from the module scheduler. Modules can be also builtin-included into the OpenSCADA core during building by an argument -enable-{ModName}=incl to the configure configuration script, what you can learn from the building manual. The OpenSCADA modules can be of seven types according to the presented modular subsystems. For now the modules to OpenSCADA are written in the "C++" programming language, although bindings for other languages may appear in the future.
At.png To create modules for OpenSCADA you need to have some experience in C/C++ programming language, the build system AutoTools, as well as basic knowledge of Linux and the distribution you are using.
In the tree of the source texts, in the branch of each subsystem, to simplify the creation of new modules, the folder "=Tmpl=" with the module template of the corresponding subsystem is provided. The developer of the new module can take this folder and copy it with the name of his new module, although he can also always use as a sample any real working module if his new one is close in structure. You can create modules in the OpenSCADA sources tree or as an independent project of the external module for OpenSCADA.
1.1 Creation in the sources tree of the OpenSCADA project
It makes sense to create new modules in the sources tree of OpenSCADA project in case of further plans for the transfer of the new module to the OpenSCADA project. Since the module should not be contrary to the spirit of the open source project and license on the basis of which OpenSCADA is developed and distributed, license of the new module obviously should be one of the free licenses.
The procedure for creating a new module with inclusion in the source text tree based on a template is generally simpler than the procedure for an external module and includes the following steps:
1. Get the source tree of the OpenSCADA project for:
  • the Work branch:
svn co svn://oscada.org/trunk/OpenSCADA
  • the stable release branch — NOT RECOMMENDED, as only patches are accepted for stable LTS releases and this instruction requires version 0.9 or higher:
svn co svn://oscada.org/tags/openscada_0.9
2. Copy the template folder with the "NewMod" name of the new module, for example, for the "DB" subsystem:
cd OpenSCADA/src/moduls/bd; cp -r =Tmpl= NewMod; cd NewMod; rm -f configure.ac
for the "DAQ" subsystem the path is — "OpenSCADA/src/moduls/daq"
for the "Archive-History" subsystem the path is — "OpenSCADA/src/moduls/arhiv"
for the "Transport" subsystem the path is — "OpenSCADA/src/moduls/transport"
for the "Transport protocol" subsystem the path is — "OpenSCADA/src/moduls/protocol"
for the "UI" subsystem the path is — "OpenSCADA/src/moduls/ui"
for the "Special" subsystem the path is — "OpenSCADA/src/moduls/special"
3. Edit the "module.cpp" file for:
also can do that automatically by: sed -i "s/Tmpl/NewMod/g" *.{cpp,h}
  • changing the name of the builtin-inclusion functions of the module according to the name of the new module:
"TModule::SAt bd_Tmpl_module( int n_mod )" —> "TModule::SAt bd_NewMod_module( int n_mod )"
"TModule *bd_Tmpl_attach( const TModule::SAt &AtMod, const string &source )" —> "TModule *bd_NewMod_attach( const TModule::SAt &AtMod, const string &source )"
  • information about the module in the "module.cpp" file, namely the section:
//* Modul info!                                  *
#define MOD_ID          "NewMod"
#define MOD_NAME        _("DB NewMod")
#define MOD_TYPE        SDB_ID
#define VER_TYPE        SDB_VER
#define MOD_VER         "0.0.1"
#define AUTHORS         _("MyName MyFamily")
#define DESCRIPTION     _("BD NewMod description.")
#define MOD_LICENSE     "GPL2"
4. Edit the module's building configuration in the "Makefile.am" file to:
also can do that automatically by: sed -i "s/Tmpl/NewMod/g" Makefile.am
EXTRA_DIST = *.h po/*
if NewModIncl
noinst_LTLIBRARIES = db_NewMod.la
db_NewMod_la_CXXFLAGS = -DMOD_INCL -fpic
db_NewMod_la_LIBTOOLFLAGS = --tag=disable-shared
db_NewMod_la_LDFLAGS = -module
else
oscd_modul_LTLIBRARIES = db_NewMod.la
db_NewMod_la_LIBTOOLFLAGS = --tag=disable-static
db_NewMod_la_LDFLAGS = -module -avoid-version $(top_builddir)/src/liboscada.la
endif
db_NewMod_la_CXXFLAGS += $(NewMod_CFLAGS)
db_NewMod_la_LDFLAGS += $(NewMod_LDLAGS)
db_NewMod_la_SOURCES = module.cpp
I18N_mod = $(oscd_modulpref)NewMod
include ../../../../I18N.mk
5. Add an entry of the new module to the end of the subsystem's section of the OpenSCADA building system configuration file "OpenSCADA/configure.ac":
  • to the section "DB modules" end for the "DB" subsystem:
AX_MOD_DB_EN(NewMod, [disable or enable[=incl] compilation module DB.NewMod], disable, incl, [
    # The code for external libraries of the module check
  • to the section "DAQ modules" end for the "DAQ" subsystem:
AX_MOD_DAQ_EN(NewMod, [disable or enable[=incl] compilation module DAQ.NewMod], disable, incl, [
  • to the section "Archive modules" end for the "Archive-History" subsystem:
AX_MOD_Archive_EN(NewMod, [disable or enable[=incl] compilation module Archive.NewMod], disable, incl, [
  • to the section "Transport modules" end for the "Transport" subsystem:
AX_MOD_Transport_EN(NewMod, [disable or enable[=incl] compilation module Transport.NewMod], disable, incl, [
  • to the section "Transport protocol modules" end for the "Transport protocol" subsystem:
AX_MOD_TrProt_EN(NewMod, [disable or enable[=incl] compilation module Protocol.NewMod], disable, incl, [
  • to the section "UI modules" end for the "UI" subsystem:
AX_MOD_UI_EN(NewMod, [disable or enable[=incl] compilation module UI.NewMod], disable, incl, [
  • to the section "Special modules" end for the "Special" subsystem:
AX_MOD_Special_EN(NewMod, [disable or enable[=incl] compilation module Special.NewMod], disable, incl, [
6. Now the new module can be built in OpenSCADA after the reorganisation of the building system:
autoreconf -if; ./configure --enable-NewMod; make
7. Publication — form a patch with your module and send it to the OpenSCADA developers:
cd OpenSCADA; make distclean; rm -rf src/moduls/bd/NewMod/{Makefile.in,.deps}
svn add src/moduls/bd/NewMod; svn diff > NewMod.patch
1.2 Creation an external module to OpenSCADA
Creation an external module to OpenSCADA may make sense in the case of the development the integration interface with business (commercial) systems that require proprietary interaction code, as well as in the case of other commercial interfaces implementations in which the module for the OpenSCADA acquire the status of the separate project, that is distributed and maintained independently often in the form of binary buildings for a specific platform and version of OpenSCADA. The license of such modules, respectively, can be arbitrary.
The procedure for creation a new external module based on the template is largely similar to the previous procedure and includes the following steps:
1. Get the source texts of the OpenSCADA project — for an external module as a source of the template you can use any OpenSCADA source files of version more than 0.9, because it is necessary to copy only the "=Tmpl=" directory and several files for build.
2. Copy the template directory with the "NewMod" name of the new module, for example, for the "DB" subsystem; and in that directory already create and copy the necessary files of the external module. Further, the information files of the project "COPYING", "NEWS", "README", "AUTHORS" and "ChangeLog" must be filled accordingly to the nature of the new module.
cp -r OpenSCADA/src/moduls/bd/=Tmpl= NewMod; touch NewMod/{NEWS,README,AUTHORS,ChangeLog}; cp OpenSCADA/I18N.mk NewMod/
for the "DAQ" subsystem the path is — "OpenSCADA/src/moduls/daq/=Tmpl="
for the "Archive-History" subsystem the path is — "OpenSCADA/src/moduls/arhiv/=Tmpl="
for the "Transport" subsystem the path is — "OpenSCADA/src/moduls/transport/=Tmpl="
for the "Transport protocol" subsystem the path is — "OpenSCADA/src/moduls/protocol/=Tmpl="
for the "UI" subsystem the path is — "OpenSCADA/src/moduls/ui/=Tmpl="
for the "Special" subsystem the path is — "OpenSCADA/src/moduls/special/=Tmpl="
3. Edit the module information in the "module.cpp" file similarly to the appropriate item in the previous section.
4. Edit the module building configuration in the "Makefile.am" file similarly to the appropriate item in the previous section, excepts:
  • instead "db_NewMod_la_LDFLAGS = -module -avoid-version $(top_builddir)/src/liboscada.la" write "db_NewMod_la_LDFLAGS = -module -avoid-version", that is remove "$(top_builddir)/src/liboscada.la"
  • instead "include ../../../../I18N.mk" write "include I18N.mk", that is remove the path "../../../../"
5. Edit the build system configuration file "configure.ac" for:
also can do that automatically by: sed -i "s/Tmpl/NewMod/g" configure.ac
  • "AC_INIT([Tmpl],[0.0.1],[my@email.org])" — information about the module: name, version and EMail of the project
  • "AM_CONDITIONAL([TmplIncl],[test])" — "AM_CONDITIONAL([NewModIncl],[test])"
6. Install the OpenSCADA development package "openscada-dev" or "openscada-devel" — because the module is an external one and the OpenSCADA source files are needed only at the first stage of the module creation, you need to install the OpenSCADA development package, which contains the header files and libraries.
7. Now you can build the new module, after formation of the building system
autoreconf -if; ./configure; make
1.3 API of the module
OpenSCADA API for the developer of OpenSCADA and modules to it is described in the document "OpenSCADA API", which should always be on hand at development for OpenSCADA. This document focuses on the detailed explanation of the main points of the modular API.
Modules in OpenSCADA are implemented as shared libraries and one such library can contain many modules of the OpenSCADA subsystems, actually acting as a container. Those containers also can be included-builtin in the OpenSCADA Core Library if you build very tightly solutions.
The first step in connecting the shared libraries (SO — Shared Object) is the connection of the initialization functions. These functions should be defined as usual "C" functions to avoid distortion of them names. Usually this is done as follows:
//================== CUT =========================
extern "C"
#ifdef MOD_INCL
#else
    TModule::SAt module( int n_mod )
#endif
        if(n_mod == 0) return TModule::SAt(MOD_ID, MOD_TYPE, VER_TYPE);
        return TModule::SAt("");
<!--T:348-->
#ifdef MOD_INCL
#else
    TModule *attach( const TModule::SAt &AtMod, const string &source )
#endif
        if(AtMod == TModule::SAt(MOD_ID,MOD_TYPE,VER_TYPE)) return new BDTmpl::BDMod(source);
        return NULL;
The entry point of any module are the following functions:
Common to all modules is the inheritance of the root object-class of the module from the class of the module subsystem TModule, which indicates the presence of a common part of the module interface, which we will consider further. To get a vision of the architecture of the modules in the context of the overall OpenSCADA architecture, it is strongly recommended to have the overall OpenSCADA class diagram in front of your eyes!
All module interface objects inherit the node class TCntrNode, which provides the control interface mechanism. One task of the mechanism is to provide the object configuration interface in any OpenSCADA configurator.
Common API
TCntrNode — OpenSCADA Node:
  • virtual void preEnable( int flag );, virtual void postEnable( int flag ); — connecting the module to the dynamic tree of objects, called before and after the actual activation of the module, respectively.
  • virtual void preDisable( int flag );, virtual void postDisable( int flag ); — excluding the module from the dynamic tree of objects before freeing the object, called before and after the actual exclusion of the module, respectively.
  • virtual void load_( TConfig *cfg );, virtual void load_( ); — loading the module from the "cfg" storage context and in general, called at the stage of loading the module configuration from the storage.
  • virtual void save_( ); — saving the module, called at the stage of saving the configuration of the module to the storage, usually at the initiative of the user.
TModule — OpenSCADA Module:
  • virtual void modStart( ); — module starting, called at the stage of starting tasks of the module's background functions, if these are provided by the module.
  • virtual void modStop( ); — stopping the module, called at the stage of stopping the tasks of performing the background functions of the module, if these are provided by the module.
  • virtual void modInfo( vector<string> &list ); — a request for a list of information properties of the module, which is provided with a standard set of properties "Module", "Name", "Type", "Source", "Version", "Author", "Description", "License", and which can be extended by own-specific properties.
  • virtual string modInfo( const string &name ); — a request for the information element name at which there performed also the requests processing of own-specific properties of the module.
  • void modFuncReg( ExpFunc *func ); — registration of the module's exported function, which is part of the mechanism of intermodule interaction that registers the internal function of the module for external call by the name-symbol of the function and its pointer relative to the object of the module. Currently, this mechanism is used by few modules!
  • virtual void perSYSCall( unsigned int cnt ); — a call from the system-service thread-task with the periodicity 10 seconds and a second counter "cnt", can be used to perform periodic-rare service procedures.
API of the modules of the "Data Bases (DB)" subsystem
Intended for the integration of OpenSCADA with a database or DBMS which is implemented by the module. Provides two common approaches in the modules implementation:
  1. ANSI SQL Mode — is the simplest way which means of direct using the core functions fieldSQLSeek(), fieldSQLGet(), fieldSQLSet(), fieldSQLDel() in fieldSeek(), fieldGet(), fieldSet(), fieldDel() respectively; all SQL-modules are used now this approach.
  2. Full Implementation — is the hardest way which means of the complete implementation; modules of such approach using are whether old or specific ones: DBF, LDAP.
TTypeBD->TModule — the root module object of the "DB" subsystem:
  • virtual string features( ); — keyword list of features supported by the DB.
  • virtual int lsPr( ); — the DB priority base [0...9] in the generic storages list.
  • virtual TBD *openBD( const string &id ); — called when a new DB object is opened or created by this module with the identifier id.
TBD — the database object:
  • virtual void enable( ); — enabling the DB.
  • virtual void disable( ); — disabling the DB.
  • virtual void allowList( vector<string> &list ) const; — requesting the table list in the DB.
  • virtual void sqlReq( const string &req, vector< vector<string> > *tbl = NULL, char intoTrans = EVAL_BOOL ); — processing the SQL-query req to the DB and receiving the result in the form of the tbl table, if the selection request and the pointer are non-zero. When intoTrans is set to TRUE, a transaction must be open for the request, and closed to FALSE. This function should be implemented for DBMSs that support SQL-queries.
  • virtual void transCloseCheck( ); — the periodically called function to check the transactions and closing the old or contain many requests ones.
  • virtual TTable *openTable( const string &name, bool create ); — called when you open or create a new table object.
TTable — the table object in the database:
  • void fieldStruct( TConfig &cfg ); — getting the current structure of the table in the object cfg.
  • bool fieldSeek( int row, TConfig &cfg, const string &cacheKey = "" ); — sequential scanning of table entries by incrementing row at the object cfg and returning FALSE after completion, with addressing by active keyUse() key fields. The cache key cacheKey is specified to prefetch the full response to the cache, extracting the following records from there.
  • void fieldGet( TConfig &cfg ); — request of the record specified in the "cfg" object with addressing by key fields.
  • void fieldSet( TConfig &cfg ); — transfer of the record specified in the "cfg" object with addressing by key fields.
  • void fieldDel( TConfig &cfg ); — deletion of the specified record by the key fields of the "cfg" object.
Specific for SQL Data Bases
  • void fieldFix( TConfig &cfg, const string &langLs = "" ); — correction of DB table structure to cfg and for translation languages langLs, usually after a failed transfer.
  • string getSQLVal( TCfg &cf, uint8_t RqFlg = 0 ); — return a SQL-specific wrapped cf value for the ReqFlg flags of the RqFlg call.
  • void setSQLVal( TCfg &cf, const string &vl, bool tr = false ); — parsing the SQL value vl to translate tr and with writing to cf.
API of the modules of the "Transports" subsystem
Provides OpenSCADA communications through the interface, often it is the network one which is implemented by the module.
TTypeTransport->TModule — the root module object of the "Transports" subsystem:
  • virtual bool isNetwork( ); — the sign of network implementation by this module.
  • virtual string outAddrHelp( ); — address format help of the output transports.
  • virtual TTransportIn *In( const string &id, const string &stor ); — called when a new input transport object is opened or created by this module with the identifier id and the storage stor.
  • virtual TTransportOut *Out( const string &name, const string &stor ); — called when a new output transport object is opened or created by this module with the identifier id and the storage stor.
TTransportIn — the input transport object:
  • virtual unsigned keepAliveReqs( ); — maximum Keep Alive requests.
  • virtual unsigned keepAliveTm( ); — keep Alive time.
  • virtual string getStatus( ); — getting the status of the transport.
  • virtual void start( ); — starting the transport.
  • virtual void stop( ); — stopping the transport.
  • virtual int writeTo( const string &sender, const string &data ); — sending data backward to the sender.
TTransportOut — the output transport object:
  • virtual string timings( ); — transport timeouts.
  • virtual unsigned short attempts( ); — connection attempts.
  • virtual void setTimings( const string &vl, bool isDef = false ); — setting the transport timeouts, as default one for isDef.
  • virtual void setAttempts( unsigned short vl ); — setting the connection attempts.
  • virtual void start( int time = 0 ); — starting the transport with the connection timeout time. When you start the output transport the actual connection to the remote station is established for the interfaces that works by the connection. At this time the errors can occur if the connection is impossible and the transport should return to the stopped state.
  • virtual int messIO( const char *oBuf, int oLen, char *iBuf = NULL, int iLen = 0, int time = 0 ); — sending of the data over the transport. The waiting timeout time of the connection in milliseconds. The time in negative disables the transport's request/respond mode and allows for the independently reading/writing to a buffer IO, with the reading timeout time in absolute.
API of the modules of the "Transport protocols" subsystem
Provides OpenSCADA with the protocol layer communications, implemented by the module, for the data access from the external systems and for the OpenSCADA data providing for the external systems.
TProtocol->TModule — the root module object of the "Transport protocols" subsystem:
  • virtual void itemListIn( vector<string> &ls, const string &curIt = "" ); — the list ls of the input protocol sub-elements from the current item curIt, if the protocol provides them. It is used when selecting an object in the input transport configuration.
  • virtual void outMess( XMLNode &io, TTransportOut &tro ); — the data transfer by the objects of the OpenSCADA core in the XML tree io to the remote system via the tro transport and the current output protocol. Presenting the data in the XML tree is non-standardized and specific to the logical structure of the protocol. This data are serialized — converted in a sequence of bytes according to the protocol, and are sent via the specified tro output transport by the messIO() function.
  • virtual TProtocolIn *in_open( const string &id ); — called when a new transport protocol object is opened or created by this module with the identifier id.
TProtocolIn — the input object of the transport protocol of the input requests processing from the input transport object TTransportIn. For each session of the input request the object of the associated input protocol is created, which remains alive until completion of the full "request->answer" session. Address of the transport, which opened the protocol instance, is specified in srcTr():
  • virtual unsigned waitReqTm( ) — the request waiting time on the input transport in milliseconds, call after what to the protocol with the empty message — the polling mode. Setting it to zero disable the polling mode.
  • virtual void setSrcTr( TTransportIn *vl ) — setting of the transport-source of the opening of the session of the input protocol.
  • virtual void setSrcAddr( const string &vl ); — setting of the sender address.
  • virtual bool mess( const string &request, string &answer ); — transfer of the request data sequence to the protocol object for it parsing accordingly to the protocol implementation. The protocol function should process the request, generate the response in answer and return FALSE in the case of the completeness of the request. If the request is not complete, it is necessary to return TRUE for the transport to indicate the "expectation of the completion", the previous parts of the request should be saved in the context of the protocol object.
API of the modules of the "Data AcQuisition" subsystem
Provides the realtime data acquisition from the external systems or it formation in the calculators, implemented by the module. That is the main subsystem since SCADA is about the Data Acquisition primarily. As the main subsystem it provides several approaches in the modules implementation, which mostly about the attributes structure formation and storing:
  1. Static formation through definition a set of the parameter types inherited from TTypeParam, that is the structures applying is performed as an attributes set with the parameter type change. This method is least flexible and it used by such modules: GPIO, SMH2Gi, AMRDevs.
  2. Dynamic formation with the structure container TElem managing in the parameter object TParamContr. This method is most flexible and used in most modules which mean of the structure be configurable.
  3. As an extension of the dynamic formation there is the Logical Level parameter type, what can be added to any module, but that used mostly in the universal data sources: LogicLev, ModBus, Siemens, OPC_UA.
TTypeDAQ->TModule — the root module object of the "Data AcQuisition" subsystem:
  • virtual bool compileFuncLangs( vector<string> *ls = NULL ); — request the list ls of languages for which it is realised the possibility of formation of user procedures in this module, and check for fact of that support.
  • virtual void compileFuncSnthHgl( const string &lang, XMLNode &shgl ); — request the rules of the syntax highlight shgl for the specified language lang.
  • virtual string compileFunc( const string &lang, TFunction &fnc_cfg, const string &prog_text, const string &usings = "", int maxCalcTm = 0 ); — compiling-registering of the user function on the supported programming language lang and on the source code of procedure prog_text, based on the procedure parameters fnc_cfg. Returns address of the compiled function's object, ready for execution.
  • virtual bool redntAllow( ); — state of support the redundancy mechanisms by the module. Should be overridden and return TRUE if supported, otherwise FALSE.
  • virtual TController *ContrAttach( const string &id, const string &daq_db ); — called when a new controller object is opened or created by this module with the identifier id.
TController — the data source controller object. In the context of the object is usually run a task of the periodic or scheduled polling of the realtime data of one physical controller or physically separated block of data. In the case of data getting by the packages, they are placed directly into the archive associated with the parameter attribute TVAl::arch(), and the current value is set by the TVAl::set() function with the attribute "sys"=TRUE:
  • virtual string getStatus( ); — request function of the controller status.
  • virtual void enable_( ); — enabling of the controller object. Usually at this stage the initialisation of the parameters' objects and their interfaces in the form of attributes is made, the attributes can sometimes be requested from the associated remote source.
  • virtual void disable_( ); — disabling the controller object.
  • virtual void start_( ); — starting the controller object. Usually at this stage the task of periodic or scheduled polling is created and started.
  • virtual void stop_( ); — stopping the controller object.
  • virtual void redntDataUpdate( ); — operation of the data receiving from the backup station, called automatically by the service procedure of the redundancy scheme of the subsystem.
  • virtual string catsPat( ); — list of the regular expression rules, separated by '|', for matching by category the messages generated by the object.
  • virtual void messSet( const string &mess, int lev, const string &type2Code = "OP", const string &prm = "", const string &cat = "" ); — formation of the DAQ-sourced messages for the parameter object prm (PrmId) or the controller object in whole if the parameter object is not specified, for the message mess, level lev and for the type code type2Code. This function generates the messages with the unified DAQ-transparency category "{type2Code}{ModId}:{CntrId}[.{prm}][:{cat}]".
  • virtual TParamContr *ParamAttach( const string &id, int type ); — called when a new object of the controller parameter is opened or created by this module with the identifier id.
TParamContr->TValue — the controller parameter object of the data source. Contains attributes with real data in a set defined by physically available data. The values to the attributes come from the polling task of the controller, in the asynchronous mode, or are requested during the access, in the synchronous mode, and through the methods of the inherited type TValue:
  • virtual TElem *dynElCntr( ); — container of the dynamic elements of the DAQ attributes. Defined mostly by the logical level sources what provide such kind containers.
  • virtual void enable( ); — enabling the parameter object, the formation of the attributes set and filling them with the value of unreliability is made.
  • virtual void disable( ); — disabling the parameter object.
  • virtual void setType( const string &tpId ); — called to change the parameter type to tpId and can be processed in the module object to change own data.
  • virtual TVal* vlNew( ); — called at the stage of a new attribute creation. Can be overridden to implement special behavior within its object, inherited from TVal, when accessing the attribute.
  • virtual void vlGet( TVal &vo ); — called for the attribute vo with the direct reading mode TVal::DirRead when reading the value in order to directly-synchronous read from the physical source or the object buffer.
  • virtual void vlSet( TVal &vo, const TVariant &vl, const TVariant &pvl ); — called for the attribute vo with the direct recording mode TVal::DirWrite when setting the value in order to directly-synchronous set to the physical source or the object buffer, with the previous value pvl.
  • virtual void vlArchMake( TVal &val ); — called at the stage of creation the values archive with the val attribute as the source in the order to initialise the qualitative characteristics of the archive buffer according to the characteristics of the data source and polling.
API of the modules of the "Archives-History" subsystem
Used for archiving and maintaining the history of messages and realtime values received in the "Data AcQuisition" subsystem, and in the means implemented by the module.
TTypeArchivator->TModule — the root module object of the "Archives-History" subsystem:
  • virtual TMArchivator *AMess( const string &id, const string &stor ); — called when a new object of the message archiver is opened or created by this module with the identifier id and in the storage stor.
  • virtual TVArchivator *AVal( const string &id, const string &stor ); — called when a new object of the value archiver is opened or created by this module with the identifier id and in the storage stor.
TMArchivator — the message archiver object.
  • virtual void start( ); — starting the archiver object, the archiver starts for receiving messages and placing them into the storage.
  • virtual void stop( ); — stopping the archiver object.
  • virtual time_t begin( ); — begin time of the archiver data accordingly with the current state of the storage.
  • virtual time_t end( ); — end time of the archiver data accordingly with the current state of the storage.
  • virtual bool put( vector<TMess::SRec> &mess, bool force = false ); — placing the message group mess to the archiver. Returns TRUE on the successful operation. Set force for direct writing to the archiver omit the redundancy.
  • virtual time_t get( time_t bTm, time_t eTm, vector<TMess::SRec> &mess, const string &category = "", char level = 0, time_t upTo = 0 ); — getting the messages to mess from the archiver for the specified filter parameters. Returns time of the request stop, useful for proceeding from this position as the end time, i.e. iteratively digging into the story. The filter specified by the time range [bTm...eTm], category rules, level and limited up to the time upTo. In the absence of a direct definition of the limiting time upTo, this limitation is set to prmInterf_TM — 7 seconds.
TVArchivator — the value archiver object.
  • virtual void start( ); — starting the archiver object, the archiver starts for receiving values and placing them into the storage.
  • virtual void stop( bool full_del = false ); — stopping the archiver object with the ability to completely remove its data from the storage at full_del.
  • virtual TVArchEl *getArchEl( TVArchive &arch ); — getting the element object of the value archive for the specified archive arch.
  • virtual void pushAccumVals( ); — pushing the accumulated values by the archivation task, for the accumulative archivers.
TVArchEl — the element object of the value archiver.
  • virtual void fullErase( ); — called to complete removal of the archive part in the archiver.
  • virtual int64_t end( ); — end time in microseconds of the available values in the archive of the archiver.
  • virtual int64_t begin( ); — begin time in microseconds of the available values in the archive of the archiver.
  • virtual TVariant getValProc( int64_t *tm, bool up_ord ); — requesting of one value from the archive for the time tm and fine-tuning to the upper value in the sampling grid up_ord.
  • virtual void getValsProc( TValBuf &buf, int64_t beg, int64_t end ); — requesting of a value group to buf from the archive and for the time range [beg...end].
  • virtual void setValsProc( TValBuf &buf, int64_t beg, int64_t end, bool toAccum ); — setting of the value group buf to the archive, for the time range [beg...end] and through the accumulation toAccum.
API of the modules of the "User Interfaces" subsystem
The user interface is formed according to the concept and mechanisms of external known standards and libraries.
TUI->TModule — the root module object of the "User Interfaces" subsystem:
At.png It contains no specific functions!
API of the modules of the "Special" subsystem
Implements the specific functions that are not included in any of the above subsystems. The specific functions are formed accordingly to their own need and with using all features of the OpenSCADA API.
TSpecial->TModule — the root module object of the "User Interfaces" subsystem:
For the convenience of direct addressing to the root object of the module from any object lower in the hierarchy, it is recommended to define the global variable "mod" in the namespace of the module, with its initialization in the constructor of the root object. Also, for transparent translation of the text messages of the module, it is recommended to define the function templates of the module message translation call "_({Message})" and "trS({Message})" as:
#undef _
#define _(mess) mod->I18N(mess).c_str()
#undef trS
#define trS(mess) mod->I18N(mess,mess_PreSave)
In the constructor of the root module's object inherited from the TModule it is necessary to set the main information of the module by call the function void modInfoMainSet({Name}, {Type}, {Version}, {Authors}, {Description}, {License}, {Source}) after init the fast link "mod" to the root object of the module.
Further receiving of the translation template file "po/oscd_NewMod.pot" of the text messages "_({Message})" and "trS({Message})", as well as updating-actualising the files of already existing translations "po/{uk|de|ru|...}.po" is carried out by the command make messages in the module folder.
During solve the tasks of the new module, it may be necessary to expand the configuration parameters, which is carried out in the virtual function void cntrCmdProc( XMLNode *req );. The content of this function, which adds properties, in the SQLite module looks like this:
void MBD::cntrCmdProc( XMLNode *opt )
    //Getting the page info
    if(opt->name() == "info") {
        TBD::cntrCmdProc(opt);
        ctrMkNode("fld",opt,-1,"/prm/cfg/ADDR",EVAL_STR,enableStat()?R_R___:RWRW__,"root",SDB_ID,3,
            "dest","sel_ed","select","/prm/cfg/dbFsList","help",
                    _("SQLite DB address must be written as: \"{FileDBPath}\".\n"
                      "Where:\n"
                      "  FileDBPath - full path to DB file (./oscada/Main.db).\n"
                      "               Use the empty path to create a temporary database on the disk.\n"
                      "               Use \":memory:\" to create a temporary database in memory."));
        if(reqCnt)
            ctrMkNode("comm",opt,-1,"/prm/st/end_tr",_("Close opened transaction"),RWRW__,"root",SDB_ID);
    //Processing for commands to the page
    string a_path = opt->attr("path");
    if(a_path == "/prm/cfg/dbFsList" && ctrChkNode(opt)) {
        opt->childAdd("el")->setText(":memory:");
        TSYS::ctrListFS(opt, addr(), "db;");
    else if(a_path == "/prm/st/end_tr" && ctrChkNode(opt,"set",RWRW__,"root",SDB_ID,SEC_WR) && reqCnt) transCommit();
    else TBD::cntrCmdProc(opt);
The first half of this function serves the "info" information requests with the list and properties of the configuration fields. The second half serves all the other commands on getting, setting value, and others. The TBD::cntrCmdProc(opt); call is used to obtain the inherited interface. More details on appointment of the used functions are in the control interface, as well as in the source code of existing modules.
The TCntrNode object, in addition to the control interface function, provides unified control mechanisms for modifying the object's configuration, loading, saving, and deleting configuration duplicates in the storage. You can use the modif() and modifG() functions to set the object data modification flag, and the module-specific loading and saving actions can be placed in virtual functions:
Configuration actions typically occur through the TConfig object, which contains a set of defined properties with structure and values. To directly reflect the properties of a module object, it inherits from TConfig, and new properties are added with the command:
fldAdd(new TFld("MOD_PRMS",trS("Module addition parameters"),TFld::String,TFld::FullText|TCfg::NoVal,"100000"));
Loading/saving/deleting of the properties specified in the TConfig object, from/to/in the storage, is made with the following commands:
TBDS::dataGet(fullDB(), owner().nodePath()+tbl(), *this);
TBDS::dataSet(fullDB(), owner().nodePath()+tbl(), *this);
TBDS::dataDel(fullDB(flag&NodeRemoveOnlyStor), owner().nodePath()+tbl(), *this, TBDS::UseAllKeys);
Where:
To generate the debug messages according the common debugging concept, you need to use the function mess_debug() with call it conditionally at the program source part:
#ifdef OSC_DEBUG
  mess_debug(...);
#endif
2 Creating new Internal Elements and Libraries with them
In order to post the library of the developed internal code to the OpenSCADA source tree repository, you must do the following and comply with the following requirements:
  • Functions, DAQ-Templates, UI-Widgets, as well as their library, must be written in the international language and contain the description itself in the description field, and general information with copyright at the end:
Author: Name Family <nick@email.org>
Total complexity: N.N HD
Version: N.N.N
License: GPLvN
  • the source texts of Functions, DAQ-Templates, UI-Widgets must be written and formatted according to some system where preference should be given to the formatting style of the main OpenSCADA modules, must not contain localised texts, but only texts in the international language wrapped with the translation function tr();
  • IO's ID and name also must be in the international language;
  • all the above texts can be translated into the Author's local language, or into several at his discretion, and on the page "Translations".
DOC: Libs_MyLib|Libs/MyLib
Besides the standard execution contexts described bottom there are provided several ones with own integration the execution context by the JavaLikeCalc Functions directly and with the possibility to select DAQ-Templates: JavaLikeCalc Controllers, ModBus Protocol DATA-Nodes, User protocol, User WWW-page. And they use own storing objects for JavaLikeCalc Functions, about which you can familiar with their own page.
The JavaLikeCalc Functions have no specific application, that is can be called from other execution contexts of OpenSCADA, from other Functions or independently by users in the service calls. So, the functions have no links and can use all the User API.
The Functions are placed and configured in libraries of the JavaLikeCalc module and each library can be stored in different storage.
DAQ-Templates
The DAQ-Templates is a part of the Logical Level conception of the Data Acquisition subsystem where the Soft Logic calculation around the obtained data is needed. But currently the DAQ-Templates also can be used in several specific OpenSCADA parts with integration the user execution context: JavaLikeCalc Controllers, ModBus Protocol DATA-Nodes, User protocol, User WWW-page. The DAQ-Templates have links on DAQ-Attributes and can use all the User API.
The Templates are placed and configured in Template Libraries of the DAQ subsystem and each library can be stored in different storage.
UI-Widgets
The UI-Widgets are a part of the VCAEngine module, which integrates the execution context. The UI-Widgets have links on DAQ-Attributes, Widget-Attributes and can use all the User API with own VCAEngine User API. Besides the standard variables, to the execution context can be directly placed attributes of the Widget and child Widgets by marking "Processing".
The Widgets are placed and configured in Widget Libraries and Projects of the VCAEngine module and each library-project can be stored in different storage.
Documents/How_to/Create_module/en - GFDLJune 2025OpenSCADA 0.9.8