| Name | Version | License | Source | Languages | Author | Description |
|---|---|---|---|---|---|---|
| Main library | 2.3 | GPLv2 | OscadaLibs.db (SQL, GZip) > DAQ.tmplb_base | en, uk, ru | Roman Savochenko | Library of the main templates of the DAQ-sources processing and related services.
|
The library was created to provide main templates of the DAQ-sources processing and related services.
The template's names and their parameters are available in languages: English, Ukrainian and mRussian. Their source code wrote in the human-language independent mode with calls for the translations by the function tr() and the message's translation also allowed for English, Ukrainian and mRussian.
For connection the library to a project of the OpenSCADA station you can obtain the database file as:
- supplied with a ready and proper package of the Linux distribution like to "openscada-libdb-main", "openscada-LibDB.Main";
- directly taken for most actual one from the subversion repository and converted to the DB SQLite file in the way:
wget http://oscada.org/svn/trunk/OpenSCADA/data/LibsDB/OscadaLibs.sql
sqlite3 -init OscadaLibs.sql OscadaLibs.db .exit
- downloaded for the one attached here.
This obtained file next you can place into the project directory of the station and create the database object for the DB module "SQLite", registering the database file in the configuration.
For the DAQ-templates at generic you need create a device representing object into the Logical Level module and select proper template from the templates library. Next, to correct configuration, follow to specific of the template into the individual description.
Contents
- 1 Templates of standard structures of the DAQ-parameters
- 1.1 Analog signal, unified (anUnif)
- 1.2 Analog signal, unified, violation statuses (anUnifSt)
- 1.3 Manual input, unified (manInUnif)
- 1.4 Discrete block, unified (digitBlockUnif)
- 1.5 Alarm discrete (digAlarm)
- 1.6 Code state (codeState)
- 1.7 PID signal, unified, violation statuses (pidUnif)
- 1.8 Impulse PID signal, unified, violation statuses (pidUnifImp)
- 2 Templates of the complex objects
- 3 Services
- 4 For WebUser
1 Templates of standard structures of the DAQ-parameters
1.1 Analog signal, unified (anUnif) |
2.4 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of analog input signals processing. The template forms a structure of analog parameter (complex tag) which can be easily connected to most widgets and cadres of the main elements library of the user interface just pointing the parameter object.
The representative structure of analog parameters (complex tags) is:
- "Variable (var)" — end variable of the parameter — engineeric real value, allowed and suitable for archiving.
- "Error (err)" — obligatory attribute of any parameter, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1, 2 — hardware errors, when the data mostly wrong;
- 3, 4 — alarm border errors;
- 5, 6 — warning border errors;
- 7 — the speed error of the variable changing.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
- "Scale: minimum (min)" and "Scale: maximum (max)" — main scale of the end variable, the output of which causes a hardware border error. The scale is also used as a scale of the variable trend display on the graphs.
- "Logarithmic scale (log)" — the scale sign of the variable trend display on the graphs in the logarithmic scale.
- "Dimension (ed)" — dimension (unit of measurement) of the variable.
- "Precision (prec)" — number signs after the dot, for positive values, and precision (signs in whole), for negative ones, to display the real end variable on the screen.
Significant graphical shapes representing the structure:
- Main elements library of the user interface:
- Mnemonic elements library of the user interface:
- Reports' and documents' library:
- Sponsored by, for expanding the common field DESCR using in the specific alarm parameters on 0.1 HD[!]: INSERTEC LTDA
Functions
- Generic processing of the raw analog input for:
- simple correction-calibration at the formula "in = iMult*(in+iAdd)";
- scaling from the hardware border [plcMin...plcMax] to the main border [min...max], applying the square scale scSqr;
-
The hardware borders can be inverted ones and disabled in whole for equal values of the maximum and minimum, when the main border only used.
- permission to exceed the border for the input value on the value of plcExcess percent;
- filtering the input value changing in the time Tf.
- Simple imitation of the analog input, setting plcImit and linking the imitation-simulation source in plcImitIn.
- Complex preprocessing and complete generation-imitation of the analog input on the internal programming language of OpenSCADA into the configuration IO inProc (with appending the builtin syntax highlight rules), where you can operate next service parameters:
- in [IN|OUT] — the same raw analog input IO;
- var [IN] — the end variable IO;
- min, max [IN] — the main border IOs;
- plcMin, plcMax [IN] — the hardware border IOs;
- plcImit, plcImitIn [IN] — IOs of the simple imitation;
- levErr, tErr [IN|OUT] — alarm level [-79...0] and text of the error (the attribute "err" format);
- f_frq [IN] — frequency of calculation, the template IO;
- this [IN] — reference to the parameter object, what executing the template;
- ctx [IN] — object of the user context, what saved between the execution cycles;
- args [IN] — object of arguments of the procedure;
- toSave [OUT] — to force save the parameter object at exit.
- Simple substitution for the variable subVar at the error (not valid) input variable (EVAL) in the modes: "no", "last" and "substitute".
- Processing the result variable var for violation some borders and criteria, generating the alarms and proper setting the attribute err. The alarm borders can have some hysteresis HystBnd, can be delayed on the time alDelay and can be suppressed setting alSup. Next borders and criteria are provided:
- missing for data or connection with source at the EVAL input value — error code 1 and alarm level 5;
- exceeding the input value of the hardware border — error code 1,2 and alarm level 5;
- exceeding the end variable of the alarm border [aMin...aMax] — error code 3,4 and alarm level 4;
- exceeding the end variable of the warning border [wMin...wMax] — error code 5,6 and alarm level 2;
- big motion speed of the end variable — error code 7 and alarm level 2.
- Specific parameters redefinition in the common attribute DESCR:
- the first line — as description of the alarm messages;
- the field CustomFlds — specifying of the custom fields of the alarm messages in the form "CustomFlds: {CustFld0} => {CustFld1} => ... => {CustFldN}";
- the field CustomAlarms — redefinition of the standard alarm levels of the alarm messages in the form "CustomAlarms: {ConErr};{BrdAlarm};{BrdWarn}".
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| in | Input | Real | Input | Not attribute | Link | Input|var |
| inProc | Input processing procedure | Text | Input | Not attribute | Constant | |
| var | Variable | Real | Input | Read only | Variable | 0 |
| ed | Dimension | String | Input | Full access | Variable | |
| min | Scale: minimum | Real | Input | Full access | Variable | 0 |
| max | Scale: maximum | Real | Input | Full access | Variable | 100 |
| scSqr | Scale: square | Boolean | Input | Full access | Variable | 0 |
| subMode | Substitute: mode | Integer numbers selection | Input | Full access | Variable | 0 0;1;2 |
| subVar | Substitute: variable | Real | Input | Full access | Variable | 0 |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| aMin | Border down alarm | Real | Input | Full access | Variable | 0 |
| aMax | Border up alarm | Real | Input | Full access | Variable | 0 |
| wMin | Border down warning | Real | Input | Full access | Variable | 0 |
| wMax | Border up warning | Real | Input | Full access | Variable | 0 |
| HystBnd | Hysteresis of borders violation | Real | Input | Full access | Variable | 1 |
| speed | Motion speed, %/cycle | Real | Input | Full access | Variable | 0 |
| prec | Precision, signs | Integer | Input | Full access | Variable | 2 |
| log | Logarithmic scale | Boolean | Input | Full access | Variable | 0 |
| Tf | Filter time, seconds | Real | Input | Full access | Variable | 0 |
| iAdd | Input addition | Real | Input | Not attribute | Constant | 0 |
| iMult | Input multiplication | Real | Input | Not attribute | Constant | 1 |
| plcMin | Minimum module scale | Real | Input | Not attribute | Constant | 0 |
| plcMax | Maximum module scale | Real | Input | Not attribute | Constant | 0 |
| plcExcess | Allowed scale exceeding, % | Real | Input | Not attribute | Constant | 0 |
| plcImit | PLC imitation | Boolean | Input | Not attribute | Constant | 0 |
| plcImitIn | PLC imitation input | Real | Input | Not attribute | Link | Imitation|var |
| this | Object | Object | Output | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- Input — link to a source of the "raw" signal.
- Input processing procedure — form for the complex preprocessing and complete generation of the analog input on the internal programming language of OpenSCADA. It is optional and should be defined in complex cases, for example:
- simple and transparent preprocessing to bring the percentage of UPS load to power that can be done with iMult also:
in = 490*in/100; //the UPS has 480W
- implementing of the input signal counter — consumed electricity of the UPS:
//Checking for the data validity
if(ctx.cntr.isEVal()) ctx.cntr = this.var.get();
if(!in.isEVal()) {
pUPS = 33;
if(ctx.cntr.isEVal()) ctx.cntr = (pUPS+in)/(3600*f_frq);
else ctx.cntr += (pUPS+in)/(3600*f_frq);
}
//Checking for the next month reset
month = 0; SYS.localtime(SYS.time(), 0, 0, 0, 0, month);
if(!ctx.month.isEVal() && month != ctx.month) ctx.cntr = 0;
ctx.month = month;
in = ctx.cntr;
- generating of the extended violations — processing for the external signals related to the source:
gO = this.cntr().prm_grps;
if(SYS.DAQ.JavaLikeCalc.lib_aviary.sensorError(gO.prm_generic.PRG_Input_Err_T_room_S.get(),levErr,tErr));
else if(!(tVl=gO.prm_alarms.PRG_Alarm_T_max.get()).isEVal() && tVl)
levErr = -4, tErr = "11:above the set limit";
else if(!(tVl=gO.prm_alarms.PRG_Alarm_T_min.get()).isEVal() && tVl)
levErr = -4, tErr = "11:below the set limit";
- Minimum and maximum of the module scale — must be set at the case of significant difference the hardware and the generic scales, for example:
- the input is raw and measured in value of the current [4...20]mA, here it is necessary to specify 4 and 20 mA;
- the previous case where it is necessary to simply and transparently calibrate the end value — with a precision device set 4mA and 20mA and indicate here the real measured values of the "raw" signal.
- Input addition and multiplication — use for easy and linear correction of the input, for example:
- calibration for the end value, which is less transparent and these coefficients should be calculated according to the formulas:
- iAdd = ((plcMin*precMeasMax)/plcMax - precMeasMin)*(plcMax/(plcMax-plcMin))
- iMult = (plcMax - plcMin) / (precMeasMax - precMeasMin)
- Allowed scale exceeding — set if necessary to exceed the value of the main border, and when this scale starts to perform the recommendation function, say for the initial display of the trend on this scale.
- PLC imitation and the imitation input — define at the need to simulate the input as required in the functions.
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: variable, error status; and the generation of violations if the state of the error is nonzero.
- 5. In the process of the working, through the tab "Attributes" of operational data, in addition to obtaining the result, it is possible to perform operative setup and control on:
- Scale: minimum and maximum — strictly
set to the range of data changes by availability and according to the hardware border, otherwise the value will be distorted! In the absence of the hardware border, this, the main border, is arbitrary and advisory, although exceeding of the border by the value will be also accompanied by a violation. - Scale: square — set if the hardware border is square one.
- Filter time — set the filtering time for noisy signals.
- Substitute: mode and variable — set the desired substitution mode at invalidity the variable.
- Violations suppress — set at the need of the parameter violations complete suppression — to disable their generation in whole.
- Violations delay — set the delay time for the generation of the violations, to exclude frequent generation, characteristic to uncertain sources of data, characterized by short-term loss of communication.
- Border up/down alarm/warning — set when it is necessary to generate violations at the exceeding of the alarm/warning borders.
- Hysteresis of borders violation — set the hysteresis of removing the violation, that is, removal of the violations occurs at the specified percentage later, in order to prevent the frequent generation by fluctuating the value near the border.
- Motion speed — set if it is necessary to warn about fast change of value.
- Name, Description, Dimension, Precision, Logarithmic scale — set this information as need when displayed, or as an element of the passport.
- Scale: minimum and maximum — strictly
1.2 Analog signal, unified, violation statuses (anUnifSt) |
1.3 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of analog input signals processing, extended by binary states of indication the violations. The template grounded on the base template "Analog signal, unified" with its representative structure and some differences characteristic to independent development and expansion.
Binary states were provided for the convenient use of algorithms of operation at the borders of violations of the parameter object, preferably in the block diagrams of general control algorithms.
Functions
Mostly the same as the basic template "Analog signal, unified" and the borderline signs are additionally provided: "H", "L", "HH", "LL", "EVAL".
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| Template IOs of "Analog signal, unified" | ||||||
| H | Border up warning violation | Boolean | Output | Read only | Variable | |
| L | Border down warning violation | Boolean | Output | Read only | Variable | |
| HH | Border up alarm violation | Boolean | Output | Read only | Variable | |
| LL | Border down alarm violation | Boolean | Output | Read only | Variable | |
| EVAL | Error value | Boolean | Output | Read only | Variable | |
Configuring and using
Completely identical to "Analog signal, unified]" with the difference of using the borderline signs: "H", "L", "HH", "LL", "EVAL"; which can be connected to external computing.
1.3 Manual input, unified (manInUnif) |
1.2 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of a manual input and an analog output signal. The template forms a structure of parameter (complex tag) of the manual input what can be easily connected to most widgets and cadres of the main elements library of the user interface just pointing the parameter object, the control mostly can be performed through the Element cadre control panel.
The representative structure of the parameter (complex tag) of the manual input is:
- "Variable (var)" — end variable of the parameter — engineeric real value, allowed and suitable for archiving.
- "Variable input (varIn)" — attribute for entering a new engineering value, which in the next falls into the variable.
- "Error (err)" — obligatory attribute of any parameter, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1, 2 — hardware errors, when the data mostly wrong;
- 3, 4 — alarm border errors;
- 5, 6 — warning border errors;
- 7 — the speed error of the variable changing.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
- "Scale: minimum (min)" and "Scale: maximum (max)" — main scale of the end variable, the output of which causes a hardware border error. The scale is also used as a scale of the variable trend display on the graphs.
- "Logarithmic scale (log)" — the scale sign of the variable trend display on the graphs in the logarithmic scale.
- "Dimension (ed)" — dimension (unit of measurement) of the variable.
- "Precision (prec)" — number signs after the dot, for positive values, and precision (signs in whole), for negative ones, to display the real end variable on the screen.
Significant graphical shapes representing the structure:
Functions
- Generic processing of the raw analog input for:
- simple correction-calibration at the formula "in = iMult*(in+iAdd)";
- scaling from the hardware border [plcMin...plcMax] to the main border [min...max], applying the square scale scSqr;
-
The hardware borders can be inverted ones and disabled in whole for equal values of the maximum and minimum, when the main border only used.
- permission to exceed the border for the input value on the value of plcExcess percent;
- filtering the input value changing in the time Tf.
- Processing the result variable var for violation some borders and criteria, generating the alarms and proper setting the attribute err. The alarm borders can have some hysteresis HystBnd, can be delayed on the time alDelay and can be suppressed setting alSup. Next borders and criteria are provided:
- missing for data or connection with source at the EVAL input value — error code 1 and alarm level 5;
- exceeding the input value of the hardware border — error code 1,2 and alarm level 5;
- exceeding the end variable of the alarm border [aMin...aMax] — error code 3,4 and alarm level 4;
- exceeding the end variable of the warning border [wMin...wMax] — error code 5,6 and alarm level 2;
- big motion speed of the end variable — error code 7 and alarm level 2.
- Reverse conversion of the engineered variable value and writing to the output.
-
In the absence of the "Input/Output" connection, the writing is not performed and there is the stand-alone operation.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| inout | Input/Output | Real | Output | Not attribute | Link | Parameter|var |
| var | Variable | Real | Input | Read only | Variable | 0 |
| varIn | Variable input | Real | Input | Full access | Variable | 0 |
| ed | Dimension | String | Input | Full access | Variable | |
| min | Scale: minimum | Real | Input | Full access | Variable | 0 |
| max | Scale: maximum | Real | Input | Full access | Variable | 100 |
| scSqr | Scale: square | Boolean | Input | Full access | Variable | 0 |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | |
| aMin | Border down alarm | Real | Input | Full access | Variable | 0 |
| aMax | Border up alarm | Real | Input | Full access | Variable | 0 |
| wMin | Border down warning | Real | Input | Full access | Variable | 0 |
| wMax | Border up warning | Real | Input | Full access | Variable | 0 |
| HystBnd | Hysteresis of borders violation | Real | Input | Full access | Variable | 1 |
| speed | Motion speed, %/cycle | Real | Input | Full access | Variable | 0 |
| prec | Precision, signs | Integer | Input | Full access | Variable | 2 |
| log | Logarithmic scale | Boolean | Input | Full access | Variable | 0 |
| Tf | Filter time, seconds | Real | Input | Full access | Variable | 0 |
| iAdd | Input addition | Real | Input | Not attribute | Constant | 0 |
| iMult | Input multiplication | Real | Input | Not attribute | Constant | 1 |
| plcMin | Minimum module scale | Real | Input | Not attribute | Constant | 0 |
| plcMax | Maximum module scale | Real | Input | Not attribute | Constant | 0 |
| plcExcess | Allowed scale exceeding, % | Real | Input | Not attribute | Constant | 0 |
| this | Object | Object | Output | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- Input/Output — link to a source of the "raw" IO signal, or do not link for the stand-alone mode.
- Minimum and maximum of the module scale — must be set at the case of significant difference the hardware and the generic scales, for example see the template "Analog signal, unified".
- Input addition and multiplication — use for easy and linear correction of the input, for example see the template "Analog signal, unified".
- Allowed scale exceeding — set if necessary to exceed the value of the main border, and when this scale starts to perform the recommendation function, say for the initial display of the trend on this scale.
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: variable, error status; and the generation of violations if the state of the error is nonzero; and it will be allowed to set new values.
- 5. In the process of the working, through the tab "Attributes" of operational data, in addition to obtaining the result, it is possible to perform operative setup and control on:
- Scale: minimum and maximum — strictly
set to the range of data changes by availability and according to the hardware border, otherwise the value will be distorted! In the absence of the hardware border, this, the main border, is arbitrary and advisory, although exceeding of the border by the value will be also accompanied by a violation. - Scale: square — set if the hardware border is square one.
- Filter time — set the filtering time for noisy signals.
- Violations suppress — set at the need of the parameter violations complete suppression — to disable their generation in whole.
- Violations delay — set the delay time for the generation of the violations, to exclude frequent generation, characteristic to uncertain sources of data, characterized by short-term loss of communication.
- Border up/down alarm/warning — set when it is necessary to generate violations at the exceeding of the alarm/warning borders.
- Hysteresis of borders violation — set the hysteresis of removing the violation, that is, removal of the violations occurs at the specified percentage later, in order to prevent the frequent generation by fluctuating the value near the border.
- Motion speed — set if it is necessary to warn about fast change of value.
- Name, Description, Dimension, Precision, Logarithmic scale — set this information as need when displayed, or as an element of the passport.
- Scale: minimum and maximum — strictly
1.4 Discrete block, unified (digitBlockUnif) |
1.0 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of the block for union of Discrete parameters for the common control device. The template forms a structure of discrete parameter-block (complex tag) which can be easily connected to most widgets and cadres of the main elements library of the user interface just pointing the parameter object.
The representative structure of discrete parameters (complex tags) is a latch object with two characteristic states and three commands, which in the final representation may have a different meaning and name:
- "State "Opened" (st_open)" — the state "Opened" of the latch. Is the primary status signal that can be used without the next one, when 1 (true) is "Opened", and 0 (false) is 'Closed'.
- "State "Closed" (st_close)" — the state "Closed".
- "Command "Open" (com)" — the command "Open" of the latch. Is the primary command signal that can be used without the next one, when 1 (true) is "Open", and 0 (false) is 'Close'.
- "Command "Close" (close)" — the command "Close" of the latch.
- "Command "Stop" (stop)" — the command "Stop" of the latch.
Significant graphical shapes representing the structure:
- Main elements library of the user interface:
- Mnemonic elements library of the user interface:
- Electrical elements library of the user interface:
Functions
- Direct obtaining, by link, of the two states (read only) and three commands (reading and writing).
- Possibility of holding the commands for a certain time and removing them.
- Ability to redefine the states and commands by the appropriate settings of the interface elements, such as digStts, for statuses, and digComs, for commands.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| com | Command "Open" | Boolean | Output | Full access | Link | com |
| close | Command "Close" | Boolean | Output | Full access | Link | close |
| stop | Command "Stop" | Boolean | Output | Full access | Link | stop |
| st_open | State "Opened" | Boolean | Input | Read only | Link | st_open |
| st_close | State "Closed" | Boolean | Input | Read only | Link | st_close |
| tCmd | Time to hold the command, seconds | Integer | Input | Not attribute | Constant | 5 |
| last_cmd | Last command | Integer | Output | Not attribute | Variable | 0 |
| w_tm | Process command counter | Real | Output | Not attribute | Variable | 0 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- All the states and commands — link to a source of the "raw" signal.
- Time to hold the command, seconds — set the desired hold value or 0 to disable this feature.
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: states and commands.
- 5. In the process of the working, through the tab "Attributes" of operational data, in addition to obtaining the result, it is possible to perform operative control, performing the commands:
1.5 Alarm discrete (digAlarm) |
1.3 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of separate discrete parameter (complex tag) processing with formation of signaling by the defined criterion. The template forms a structure of discrete parameter (complex tag) which can be easily connected to most widgets and cadres of the main elements library of the user interface just pointing the parameter object.
The template provides some fields of the representative structure of the discrete parameters and adds the error field:
- "State "Opened" (st_open)" — the state "Opened".
- "State "Closed" (st_close)" — the state "Closed".
- "Error (err)" — obligatory attribute of any parameter, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1 — hardware errors, when the data mostly wrong;
- 3 — violation of the specified condition.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
Functions
- Direct obtaining, by link, of the initial state and formation of two representative states with the possibility of their inversion stInv.
- Complex preprocessing and complete generation-imitation of the discrete input on the internal programming language of OpenSCADA into the configuration IO inProc (with appending the builtin syntax highlight rules), where you can operate next service parameters:
- in [IN|OUT] — the same raw discrete input IO;
- levErr, tErr [IN|OUT] — alarm level [-79...0] and text of the error (the attribute "err" format);
- f_frq [IN] — frequency of calculation, the template IO;
- this [IN] — reference to the parameter object, what executing the template;
- ctx [IN] — object of the user context, what saved between the execution cycles;
- args [IN] — object of arguments of the procedure.
- Processing of the discrete input in for the purpose of creating a violation and correspondingly setting the attribute err, at the condition "{st}:{lev}:{mess}", that is violation generation of the level lev and the text mess for the input status st (0|1). What can be delayed on the time alDelay and can be suppressed setting alSup.
- Specific parameters redefinition in the common attribute DESCR:
- the first line — as description of the alarm messages;
- the field CustomFlds — specifying of the custom fields of the alarm messages in the form "CustomFlds: {CustFld0} => {CustFld1} => ... => {CustFldN}".
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| alrm | Alarm "{st}:{lev}:{mess}" | String | Input | Not attribute | Constant | |
| stInv | State inversion | Boolean | Input | Not attribute | Constant | |
| in | Input | Boolean | Input | Read only | Link | Input|in |
| inProc | Input processing procedure | Text | Input | Not attribute | Constant | |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| st_open | State "Opened" | Boolean | Input | Read only | Variable | |
| st_close | State "Closed" | Boolean | Input | Read only | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| this | Object | Object | Input | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- "Alarm "{st}:{lev}:{mess}" — define the criterion for the violation formation, leave blank to disable the violations generation.
- "State inversion" — set to invert the representative attributes, that is, "st_open" set for "in" equal to false.
- Input — link to a source of the "raw" signal.
- Input processing procedure — form for the complex preprocessing and complete generation of the discrete input on the internal programming language of OpenSCADA. For example:
- complete creation for a complex status:
gO = this.cntr().prm_grps;
status = gO.prm_generic.PRG_Input_Err_T_Zone1_S.get();
in = gO.prm_generic.SET_CalcFan_UseSensor_T1.get() || !(status == 0 || status == 2 || status == 3);
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: variable, error status; and the generation of violations if the state of the error is nonzero.
1.6 Code state (codeState) |
1.4 | GPLv2 | * | en, uk, ru | Roman Savochenko |
A variant of the common, representative and unified template of the block for union of Discrete parameters, expanded by more than two states and three commands that can be encoded by an integer value. The template forms a structure of parameter (complex tag) which can be easily connected to most widgets and cadres of the main elements library of the user interface just pointing the parameter object.
- Sponsored by: Vinnica Poultry Farm
The representative structure of the parameter (complex tag) of the code state is:
- "State "Text" (st_text)" — text description of the state.
- "Command "Text" (com_text)" — text of the command.
- "Commands (digComs)" — common list of the allowed commands, to form the selecting.
- "Error (err)" — obligatory attribute of any parameter, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1 — hardware errors, when the data mostly wrong.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
Significant graphical shapes representing the structure:
Functions
- Direct receiving, by link, the status code and the command (read only), as well as setting the status text according to the list of states stats.
- Working out the text of the command com_text to find it in the general list coms of commands and issuing the received command code to the output.
- Generating from the general list coms of commands the list of commands to be selected in digComs.
- Complex processing and complete generation-imitation of the code state, as well as processing the code or the command text for targeted actions, on the internal programming language of OpenSCADA into the configuration IO inProc, where you can operate next service parameters:
- in [IN|OUT] — IO of the code state;
- text [OUT] — direct text status setting;
- coms [IN] — list of available commands, of the corresponded IO;
- com_text [IN|OUT] — text of the received command;
- levErr, tErr [IN|OUT] — alarm level [-79...0] and text of the error (the attribute "err" format);
- f_frq [IN] — frequency of the calculation, the template IO;
- this [IN] — reference to the parameter object, what executing the template;
- ctx [IN] — object of the user context, what saved between the execution cycles;
- args [IN] — object of arguments of the procedure.
- Formation of the violation and the corresponding setting of the attribute err, provided at setting in the processing procedure or lack of the communication (in = EVAL). What can be delayed on the time alDelay and can be suppressed setting alSup.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| in | Input | Integer | Input | Read only | Link | Signal|in |
| out | Output | Integer | Output | Read only | Link | Signal|out |
| inProc | Input processing procedure | Text | Input | Not attribute | Constant | |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| st_text | State "Text" | String | Input | Read only | Variable | |
| stats | States, rows "{code}:{State}" | Text | Input | Full access | Variable | |
| com_text | Command "Text" | String | Input | Full access | Variable | |
| coms | Commands-states, rows "{code}:{State}" | Text | Input | Full access | Variable | |
| digComs | Commands | Text | Input | Read only | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| this | Object | Object | Output | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- Input and Output — link to a source of the "raw" signal.
- Input processing procedure — form for the processing and complete generation-imitation of the input, and issuing of the specific output, on the internal programming language of OpenSCADA. For example:
- complete creation for the state code and alarms forming:
gO = this.cntr().prm_grps;
if(gO.prm_fansControl.PRG_CntrFan_AutoMode_G1.get().isEVal()) in = 4;
else {
if(!(tVl=gO.prm_fansControl.PRG_CntrFan_Alarm_ThermalRelay.get()).isEVal() && tVl)
levErr = -4, tErr = "11:alarm";
if(gO.prm_fansControl.PRG_CntrFan_AutoMode_G1.get())
in = gO.prm_fansControl.PRG_CntrFan_On_G1.get() ? 1 : 2;
else in = 3;
}
- forming the clock time text and issuing the time synchronization — direct status text setting and issuing for specific commands:
curTm = SYS.time();
text = SYS.strftime(curTm, "%H։%M %d.%m.%Y");
gO = this.cntr().prm_grps;
if(!(tVl=gO.prm_other.PRG_RTC_UNIX.get()).isEVal()) {
text += " ("+(tVl-curTm).toString(10,0,true)+")";
}
if(com_text.length && !com_text.isEVal() && (tVl=coms.match("^([^:]+):"+com_text,"m")).length && tVl[1] == 1) {
gO.prm_other.SET_RTC_New_UNIX.set(curTm);
gO.prm_other.KEY_RTC_set_time.set(true);
}
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: input, output, code-input state, error status; and the generation of violations if the state of the error is nonzero.
- 5. In the process of the working, through the tab "Attributes" of operational data, in addition to obtaining the result, it is possible to perform operative control, performing the commands:
- States — set to list of accordance with its status code to text.
- Commands-states — set to list of accordance with its status-command code to text.
- Command "Text" — set in the command text, which is described in the command list, for the code conversion and issuance.
- Violations suppress — set at the need of the parameter violations complete suppression — to disable their generation in whole.
- Violations delay — set the delay time for the generation of the violations, to exclude frequent generation, characteristic to uncertain sources of data, characterized by short-term loss of communication.
1.7 PID signal, unified, violation statuses (pidUnif) |
1.2 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of an interface to the Proportional Integral Differential (PID) regulator based on the common analog input signal, extended by binary states of indication the violations. The template forms a structure of the analog PID-regulator which can be easily connected to some cadres and widgets of the main elements library of the user interface just pointing the parameter object.
- Sponsored by: DIYA Ltd
The representative structure of the analog PID-regulators is:
- "Variable (var)" — end variable of the parameter — engineeric real value, allowed and suitable for archiving.
- "Error (err)" — obligatory attribute of any parameter, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1, 2 — hardware errors, when the data mostly wrong;
- 3, 4 — alarm border errors;
- 5, 6 — warning border errors;
- 7 — the speed error of the variable changing.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
- "Setpoint (sp)" — setpoint for the analog signal value achievement in the automatic mode.
- "Manual input (manIn)" — attribute for entering a new output value, which in the next falls into the output at the manual mode.
- "Output (out)" — output (control signal) of the PID-regulator.
- "Mode: automate (auto)" — the PID-regulator mode "Automatic".
- "Mode: cascade (casc)" — the PID-regulator mode "Cascade".
- "Scale: minimum (min)" and "Scale: maximum (max)" — main scale of the end variable, the output of which causes a hardware border error. The scale is also used as a scale of the variable trend display on the graphs.
- "Logarithmic scale (log)" — the scale sign of the variable trend display on the graphs in the logarithmic scale.
- "Dimension (ed)" — dimension (unit of measurement) of the variable.
- "Precision (prec)" — number signs after the dot, for positive values, and precision (signs in whole), for negative ones, to display the real end variable on the screen.
Significant graphical shapes representing the structure:
Functions
- Generic processing of the raw analog input for:
- simple correction-calibration at the formula "in = iMult*(in+iAdd)";
- scaling from the hardware border [plcMin...plcMax] to the main border [min...max], applying the square scale scSqr;
- permission to exceed the border for the input value on the value of plcExcess percent;
- filtering the input value changing in the time Tf.
- Simple imitation of the analog input, setting plcImit and linking the imitation-simulation source in plcImitIn.
- Processing the result variable var for violation some borders and criteria, generating the alarms and proper setting the attribute err. The alarm borders can have some hysteresis HystBnd, can be delayed on the time alDelay and can be suppressed setting alSup. Next borders and criteria are provided:
- missing for data or connection with source at the EVAL input value — error code 1 and alarm level 5;
- exceeding the input value of the hardware border — error code 1,2 and alarm level 5;
- exceeding the end variable of the alarm border [aMin...aMax] — error code 3,4 and alarm level 4;
- exceeding the end variable of the warning border [wMin...wMax] — error code 5,6 and alarm level 2;
- big motion speed of the end variable — error code 7 and alarm level 2.
- Transmission of the PID-specific information, control and coefficient attributes to and from the PLC or other data source with the regulation.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| in | Input | Real | Input | Not attribute | Link | Signal|in |
| sp | Setpoint | Real | Input | Full access | Link | PID|sp |
| var | Variable | Real | Input | Read only | Variable | 0 |
| manIn | Manual input, % | Real | Input | Full access | Link | PID|manIn |
| out | Output, % | Real | Input | Full access | Link | PID|out |
| auto | Mode: automate | Boolean | Input | Full access | Link | PID|auto |
| casc | Mode: cascade | Boolean | Input | Full access | Link | PID|casc |
| ed | Dimension | String | Input | Full access | Variable | |
| min | Scale: minimum | Real | Input | Full access | Link | PID|min |
| max | Scale: maximum | Real | Input | Full access | Link | PID|max |
| scSqr | Scale: square | Boolean | Input | Full access | Variable | 0 |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | 0 |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| aMin | Border down alarm | Real | Input | Full access | Variable | 0 |
| aMax | Border up alarm | Real | Input | Full access | Variable | 0 |
| wMin | Border down warning | Real | Input | Full access | Variable | 0 |
| wMax | Border up warning | Real | Input | Full access | Variable | 0 |
| HystBnd | Hysteresis of borders violation | Real | Input | Full access | Variable | 0 |
| speed | Motion speed, %/cycle | Real | Input | Full access | Variable | 0 |
| prec | Precision, signs | Integer | Input | Full access | Variable | 2 |
| log | Logarithmic scale | Boolean | Input | Full access | Variable | 0 |
| H | Border up warning violation | Boolean | Output | Read only | Variable | 0 |
| L | Border down warning violation | Boolean | Output | Read only | Variable | 0 |
| HH | Border up alarm violation | Boolean | Output | Read only | Variable | 0 |
| LL | Border down alarm violation | Boolean | Output | Read only | Variable | 0 |
| EVAL | Value is error | Boolean | Output | Read only | Variable | 0 |
| Tf | Filter time, milliseconds | Real | Input | Full access | Variable | 0 |
| Kp | Gain | Real | Input | Full access | Link | PID|Kp |
| Ti | Ti, milliseconds | Integer | Input | Full access | Link | PID|Ti |
| Kd | Gain differential | Real | Input | Full access | Link | PID|Kd |
| Td | Td, milliseconds | Integer | Input | Full access | Link | PID|Td |
| Tzd | T differential lag, milliseconds | Integer | Input | Full access | Link | PID|Tzd |
| Zi | Insensitivity, % | Real | Input | Full access | Link | PID|Zi |
| Hup | Upper output border, % | Real | Input | Full access | Link | PID|Hup |
| Hdwn | Lower output border, % | Real | Input | Full access | Link | PID|Hdwn |
| K1 | Coefficient of input 1 | Real | Input | Full access | Link | PID|K1 |
| K2 | Coefficient of input 2 | Real | Input | Full access | Link | PID|K2 |
| K3 | Coefficient of input 3 | Real | Input | Full access | Link | PID|K3 |
| K4 | Coefficient of input 4 | Real | Input | Full access | Link | PID|K4 |
| iAdd | Input addition | Real | Input | Not attribute | Constant | 0 |
| iMult | Input multiplication | Real | Input | Not attribute | Constant | 1 |
| plcMin | Minimum module scale | Real | Input | Not attribute | Constant | 1 |
| plcMax | Maximum module scale | Real | Input | Not attribute | Constant | 5 |
| plcExcess | Allowed scale exceeding, % | Real | Input | Not attribute | Constant | 0 |
| plcImit | PLC imitation | Boolean | Input | Not attribute | Constant | 0 |
| plcImitIn | PLC imitation input | Real | Input | Not attribute | Link | Imitation|var |
| this | Object | Object | Output | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. Into the tab "Template configuration" of the logical parameter object you need to set:
- Input — link to a source of the "raw" analog signal.
- Setpoint, Manual input, Output, Mode: automate, Mode: cascade, Scale: minimum, Scale: maximum, Gain, Ti, Gain differential, Td, T differential lag, Insensitivity, Upper output border, Lower output border, Coefficient of input 1, Coefficient of input 2, Coefficient of input 3, Coefficient of input 4 — link to a source of the PID-regulator.
- Input addition and multiplication — use for easy and linear correction of the input, for example see the template "Analog signal, unified".
- Allowed scale exceeding — set if necessary to exceed the value of the main border, and when this scale starts to perform the recommendation function, say for the initial display of the trend on this scale.
- PLC imitation and the imitation input — define at the need to simulate the input as required in the functions.
- 4. RESULT: Launching the controller object (where this parameter is created) and if it has not been started, we must get the operational data in the tab "Attributes" for: variable, error status; and the generation of violations if the state of the error is nonzero. Also we will get all the PID-specific attributes.
- 5. In the process of the working, through the tab "Attributes" of operational data, in addition to obtaining the result, it is possible to perform operative setup and control on:
- Scale: minimum and maximum — strictly
set to the range of data changes by availability and according to the hardware border, otherwise the value will be distorted! - Scale: square — set if the hardware border is square one.
- Filter time — set the filtering time for noisy signals.
- Violations suppress — set at the need of the parameter violations complete suppression — to disable their generation in whole.
- Violations delay — set the delay time for the generation of the violations, to exclude frequent generation, characteristic to uncertain sources of data, characterized by short-term loss of communication.
- Border up/down alarm/warning — set when it is necessary to generate violations at the exceeding of the alarm/warning borders.
- Hysteresis of borders violation — set the hysteresis of removing the violation, that is, removal of the violations occurs at the specified percentage later, in order to prevent the frequent generation by fluctuating the value near the border.
- Motion speed — set if it is necessary to warn about fast change of value.
- Name, Description, Dimension, Precision, Logarithmic scale — set this information as need when displayed, or as an element of the passport.
- Scale: minimum and maximum — strictly
1.8 Impulse PID signal, unified, violation statuses (pidUnifImp) |
1.1 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Common, representative and unified template of an interface to the Proportional Integral Differential (PID) regulator based on the common analog input signal but with the PWM-output, extended by binary states of indication the violations and mostly like to the template "PID signal, unified, violation statuses". The template forms a structure of the impulse PID-regulator which can be easily connected to some cadres of the main elements library of the user interface just pointing the parameter object.
- Sponsored by: DIYA Ltd
The representative structure of the impulse PID-regulators is mostly equal to the template "PID signal, unified, violation statuses" and contains a number of attributes specific to the pulse output and the attribute of determining the operation of this regulator in the analog mode, that is, this template is even more generalizable:
- "Impulse output up (impQup)" and "Impulse output down (impQdwn)" — signals of the PWM-output.
- "Mode: analog (analog)" — a sign of working the regulator in the analog output mode.
Functions
Mostly the same as the basic template "PID signal, unified, violation statuses" and the impulse-specific attributes are additionally provided: "Impulse output up", "Impulse output down", "Mode: analog", "T impulses period", "T minimal impulse", "Impulse rate factor".
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| Template IOs of "PID signal, unified, violation statuses" | ||||||
| impQup | Impulse output up | Boolean | Input | Read only | Link | PID|impQupTm |
| impQdwn | Impulse output down | Boolean | Input | Read only | Link | PID|impQdwnTm |
| analog | Mode: analog | Boolean | Input | Read only | Link | PID|analog |
| TImpPer | T impulses period, milliseconds | Integer | Input | Full access | Link | PID|TImpPer |
| TImpMin | T minimal impulse, milliseconds | Integer | Input | Full access | Link | PID|TImpMin |
| KImpRfact | Impulse rate factor | Real | Input | Full access | Link | PID|KImpRfact |
Configuring and using
Mostly the same as the basic template "PID signal, unified, violation statuses" with the difference of using the impulse specific output: "Impulse output up", "Impulse output down", "Mode: analog", "T impulses period", "T minimal impulse", "Impulse rate factor".
2 Templates of the complex objects
In some cases where an object is only a part of a common automated system and does not require deep detailing to the level of signals and parameters (complex tag) around them, including without the need for archiving, it is convenient to unify them in one representative object of the data source OpenSCADA with appropriate consolidated view and object control as a set of simple attributes with violation elements. Such consolidation often occurs around specialised data sources, whose access to data is usually implemented through a separate exchanging protocol, but without unifying the transmission of this data to the level of visualisation and signalling by a separate attribute of the object.
In general, the representative structure of a complex object is:
- "All items (items)" — common object-type attribute where the attributes of a physical object are directly described by object-type attributes in items and with defined descriptive attributes in each
- id — attribute identifier;
- descr — text description of the attribute;
- wr — a sign of the possibility of writing or a list of value variants to their selection, through the symbol ';';
- alarm — violation code:
- 0 — no violation — "NORM";
- 1 — violation level "WARNING";
- 2 — violation level "ALARM";
- val — attribute value;
- set — attribute value to set the attributes accessible to write.
- "Error (err)" — obligatory attribute of common violation status of the object in general, consist of the combination of the error code and short text description, like to "2:No data or connection with source". The template reserves next error codes:
- 1 — violation level "WARNING";
- 2 — violation level "ALARM";
- 3 — unreliability or lack of data.
- "Violations suppress (alSup) and delay (alDelay)" — violations generic control for suppressing and delaying.
Generally, it is advisable to create such template (a layer above the physical data source object) above a raw data source that provides this data in attributes and without processing, and this template therefore performs:
- collection of these attributes of the raw source into items;
- processing of properties of the attributes;
- control and transmitting of commands of the values setting;
- processing of the violation conditions at single attributes and at the object in whole, together with which these violations can be fixed in the table of actual violations, typically by the alarmSet() function.
In addition to complex object templates, this object-control mechanism can be implemented by templates for implementing the logical level of data access, such as in IEC60870.
To represent the data of the object-control mechanism, there currently provided the appropriate Object properties frame, which provides these properties as a table-list with illumination of the violations and the possibility to change the selected and accessible to edit row-properties.
2.1 Uninterruptible Power Supply (UPS) |
2.2 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Data combination of the Uninterruptible Power Supply in a complex object of the attribute "All items". The template initially designed to use together with the DAQ-module "System" in the part "UPS" and to represent this data by the frame "Object properties" as a complex object with properties, signalling at single borders and writing.
Next the template was expanded by direct implementing UPS or Power Inverters which support is missing in NUT (in ground of the part "UPS"), and such the first device became Must EP2100 PRO. And for that there also was appended of custom definition the device's properties to place as DAQ-Attributes with the possibility of the description redefinition.
- Sponsored by: DIYA Ltd
Template IOs
| Identifier | Parameter | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| srcAddr | Source object's address
|
String | Input | Not attribute | Constant | |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| items | All items | Object | Output | Full access | Variable | |
| defs | Elements definition
In form of lines - "{id}:{toAttr}:{descr}" |
Text | Output | Full access | Variable | |
| bChL | Battery charge low | Real | Input | Full access | Variable | 20 |
| bChLL | Battery charge critical | Real | Input | Full access | Variable | 5 |
| inVL | Input voltage low | Real | Input | Full access | Variable | 210 |
| inVH | Input voltage high | Real | Input | Full access | Variable | 250 |
| inFLL | Input frequency too low | Real | Input | Full access | Variable | 40 |
| inFL | Input frequency low | Real | Input | Full access | Variable | 45 |
| inFH | Input frequency high | Real | Input | Full access | Variable | 55 |
| inFHH | Input frequency too high | Real | Input | Full access | Variable | 60 |
| loadH | Load high | Real | Input | Full access | Variable | 80 |
| loadHH | Load too high | Real | Input | Full access | Variable | 100 |
| tH | Temperature high | Real | Input | Full access | Variable | 50 |
| tHH | Temperature too high | Real | Input | Full access | Variable | 70 |
| hyst | Hysteresis of borders, % | Real | Input | Full access | Variable | 5 |
| this | Object | Object | Input | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. [ DAQ.System ] Create a source controller object in the module DAQ.System and set its identifier like to "SYSData".
- 2. [ DAQ.System ] Create a source parameter object in the previous controller object and set its identifier like to "UPS".
- 3. Create and start a Logical Controller Object or use any presented with the need scheduling properties.
- 4. Create a Logical Parameter Object and select the template for it. Enable the parameter.
- 5. In the tab "Template configuration" of the Logical Parameter Object you need to set:
- Source object's address:
- [ DAQ.System ] — to address of the source UPS parameter object (see to step 1) like to "System.SYSData.prm_UPS";
- [ Must EP2100 PRO ] — to Serial address of connecting the device like to "Serial.ep21:/dev/ttyUSB0:9600:8N1||500:30".
- 6. RESULT: When running the controller object (where this parameter was created) and if it was not started, we must obtain in the parameter attribute All items (items) this object with all the attributes and their properties. In the case of some violations, we will get the corresponding information in the attribute Error (err), for which you can adjust the attributes of the boundaries of the corresponding violations. To customize some item's description and to place some in DAQ-Attributes, you can edit "Elements definition (defs)" for ones. From the created DAQ-Attributes you can also control writable ones.
- 7. In the visual interfaces developing of the module Vision place the frame "Object properties" to any page and link its to the parameter object, created in step 4.
- 8. RESULT: In the runtime of the page you'll get a table with data of the object, notifications about violations in the header and the possibility to set of writable properties.
2.2 Network devices by SNMP (SNMP) |
1.1 | GPLv2 | * | en, uk, ru | Roman Savochenko |
Data combination of a device, accessible by the protocol SNMP, in a complex object of the attribute "All items". The template designed to use together with the DAQ-module "SNMP" and to represent this data by the frame "Object properties" as a complex object with properties, signalling at single borders and writing. Considering the great specificity and variety of SNMP-accessible devices, this template is actually a billet and an example of creating a template based on it to a corresponding device with a specific to it processing of input properties, forming of violations and write capability.
- Sponsored by: PAC HARTRON
Template IOs
| Identifier | Parameter | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| srcAddr | Source object's address | String | Input | Not attribute | Constant | |
| manTables | Manual tables | String | Input | Not attribute | Constant | |
| alSup | Violations suppress | Boolean | Input | Full access | Variable | |
| alDelay | Violations delay, seconds | Real | Input | Full access | Variable | 0 |
| items | All items | Object | Output | Full access | Variable | |
| this | Object | Object | Input | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String (translate) | Input | Not attribute | Variable | |
| DESCR | Description | Text (translate) | Input | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
Configuring and using
- 1. Create a source controller object in the module "SNMP" and set its identifier like to "SYSData".
- 2. Create a source parameter object in the previous controller object and set its identifier like to "DEV".
- 3. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 4. Create a logical parameter object and select the template for it. Enable the parameter.
- 5. In the tab "Template configuration" of the logical parameter object you need to set:
- Source object's address — to address of the source SNMP device parameter object (see to step 1) like to "SNMP.SYSData.DEV".
- Manual tables — enter manually some static MIB-variables.
- 6. RESULT: When running the controller object (where this parameter was created) and if it was not started, we must obtain in the parameter attribute items this object with all the attributes and their properties. In case of some violations, we will get the corresponding information in the attribute of the parameter err, for which you can adjust the attributes of the boundaries of the corresponding violations.
- 7. In the visual interfaces developing of the module Vision place the frame "Object properties" to any page and link it to the parameter object, created in step 4.
- 8. RESULT: In runtime of the page you get a table with data of the object, notifications about violations in the header and the possibility to set of writable properties.
2.3 Disk SMART (DiskSMART) |
1.1 | GPLv2 | * | en, uk | Roman Savochenko |
Data combination of the disk SMART in a complex object of the attribute "All items". The template designed to use together with the DAQ-module "System" in the part "Disk SMART" and to represent this data by the frame "Object properties" as a complex object with properties and signalling at common errors. Some SMART attributes can be unknown or wrong for specified disk due to their missing in the disks DB, especially for modern SSD, so the template provides a feature to redefine names the attributes.
Complex postprocessing and complete generation-imitation of the SMART fields with separate attributes on the internal programming language of OpenSCADA into the configuration IO inProc (with appending the builtin syntax highlight rules), where you can operate next service parameters:
- alLev, tErr [IN|OUT] — alarm level [-79...0] and text of the error (the attribute "err" format);
- f_frq [IN] — frequency of calculation, the template IO;
- this [IN] — reference to the parameter object, what executing the template;
- ctx [IN] — object of the user context, what saved between the execution cycles;
- args [IN] — object of arguments of the procedure;
- items [IN|OUT] — object of items of the SMART.
Template IOs
| Identifier | Parameter | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| srcAddr | Source object's address | String | Input | Not attribute | Constant | |
| inProc | Input processing procedure | Text | Input | Not attribute | Constant | |
| items | All items | Object | Output | Full access | Variable | |
| defs | Item definitions | Text | Input | Full access | Variable |
161:Number of Valid Spare Blocks (161) 162:Uncorrectable Sector Count (162) 163:Number of Initial Invalid Blocks (163) 164:Total Erase Count (164) 165:Block Erase Count (165) 166:Minimum PE Cycles TLC (166) 167:Max Bad Blocks per Die (167) 168:Maximum PE Cycles TLC (168) 168:Max Erase Count of Spec (168) 168:SATA PHY error count (168) 169:Total Bad Blocks (169) 169:Remain Life (169) 170:Grown Bad Blocks (170) 170:Bad Block Count (170) 171:Program Fail Count (171) 172:Erase Fail Count (172) 173:Average PE Cycles TLC (173) 173:Max Erase Count (173) 174:Unexpected Power Loss (174) 184:End-to-End Error (184) 187:Reported Uncorrect (187) 188:Command Timeout (188) 218:CRC Error Count (218) 230:Media Wearout Indicator (230) 231:SSD Life Left (231) 233:NAND GB Written TLC (233) 234:NAND GB Written SLC (234) 241:Host Writes GB (241) 242:Host Reads GiB (242) 244:Temp Throttle Status (244) 245:Flash Write Sector Count (245) |
| this | The object | Object | Input | Not attribute | Variable | |
| SHIFR | Code | String | Input | Not attribute | Variable | |
| NAME | Name | String | Input | Not attribute | Variable | |
| DESCR | Description | String | Input | Not attribute | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
Configuring and using
- 1. Create a source controller object in the module "System" and set its identifier like to "SYSData", set the property "Auto create active data sources" to "All sources" and start by setting "Running".
- 2. Create and start a logical controller object or use any presented one with the need scheduling properties.
- 3. Create a logical parameter object and select the template for it. Enable the parameter.
- 4. In the tab "Template configuration" of the logical parameter object you need to set:
- Source object's address — to address of the source disk SMART parameter object like to "System.SYSData.DiskSMARTsda".
- Input processing procedure — form for the complex preprocessing and complete generation of the SMART fields with separate attributes on the internal programming language of OpenSCADA.
- 5. RESULT: When running the controller object (where this parameter was created) and if it was not started, we must obtain in the parameter attribute items this object with all the attributes and their properties. In case of some violations, we will get the corresponding information in the attribute of the parameter err.
- 6. In the visual interfaces developing of the module Vision place the frame "Object properties" to any page and link it to the parameter object, created in step 3.
- 7. RESULT: In runtime of the page you get a table with data of the object, notifications about violations in the header and the possibility to redefine names of the SMART attributes.
3 Services
3.1 Notificator by SMS, EMail-SMTP (ntf) |
1.0 | GPLv2 | * => UserProtocol | en, uk, ru | Roman Savochenko |
The complex template of the notification contains of parts of the dispatcher and the output user protocol of notification by EMail(SMTP) and SMS.
- Total complexity: > 1.05 HD[!]
- Sponsored by, for initial implementation the SMS-send part on 0.2 HD[!]: Oleg Sidashov
- Sponsored by, for unification, appending SMTP and the notification controller on 0.65 HD[!]: SVItoVYR Ltd
THE DISPATCHER can be performed for pointed messages of the message buffer of OpenSCADA and applied on the Logical level or the controller object of the module JavaLikeCalc.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| io | UserPrt: Output IO | Object | Input | Not attribute | Variable | |
| tr | UserPrt: Transport | Object | Input | Not attribute | Variable | |
| tmOut | Maximum notification timeout, seconds | Integer | Input | Not attribute | Constant | 5 |
| messLev | Messages level, negative for alarms | Integer | Input | Not attribute | Constant | 1 |
| messCat | Messages category, template or regular expression | String | Input | Not attribute | Constant | al*:* |
| messCatExcl | Message exclusion category, in regular expression | String | Input | Not attribute | Constant | |
| emailState | Email notification current state | String | Output | Read only | Variable | |
| emailTrAddr | Output transport for SMTP connection, empty for disable | String | Input | Not attribute | Constant | Sockets.out_SMTP |
| emailAuth | Auth, empty for disable | String | Input | Not attribute | Constant | user:pass |
| emailSender | Sender | String | Input | Not attribute | Constant | noreply@oscada.org |
| emailReceiver | Destination receiver address | String | Input | Not attribute | Constant | test@oscada.org |
| emailTopic | EMail topic | String | Input | Not attribute | Constant | Notification |
| emailMess | EMail message | String | Input | Not attribute | Constant | |
| SMSState | SMS notification current state | String | Output | Read only | Variable | |
| SMSTrAddr | SMS serial transport, empty for disable | String | Input | Not attribute | Constant | Serial.out_SMS |
| SMSPin | SMS-pin, empty for disable | String | Input | Not attribute | Constant | 1111 |
| SMSTel | SMS destination receiver, tel. number | String | Input | Not attribute | Constant | +380XXXXXXXXX |
| SMSTextMd | SMS in the text mode, else PDU | Boolean | Input | Not attribute | Constant | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create a parameter in a controller object of the Logical Level or a controller object in the module DAQ.JavaLikeCalc.
- 2. Create an output transport of the type "Serial" and set its Identifier like to "SMS", one transport suitable for more receivers.
- 3. Set for proper address, only for the Serial device. The serial port speed, asynchronous data format and timeouts will adjusted by the function.
- 4. Create an output transport of the type "Sockets" or "SSL" and set its Identifier like to "SMTP", one transport suitable for more receivers.
- 5. Set-up for proper address, for Sockets(25) or SSL(465). The transport timeouts will be adjusted by the function.
- 6. In the tab "Template configuration" you need to set:
- Maximum notification timeout, seconds.
- Messages level, negative for alarms.
- Messages category, template or regular expression.
- Message exclusion category, in regular expression.
- Output transport for SMTP connection, empty for disable.
- Auth, empty for disable.
- Sender.
- Destination receiver address.
- EMail topic.
- EMail message.
- SMS serial transport, empty for disable.
- SMS-pin, empty for disable.
- SMS destination receiver, tel. number.
- SMS in the text mode, else PDU.
- 7. RESULT: Sending for the pointed messages at SMS or EMail(SMTP).
THE OUTPUT USER PROTOCOL PART "SMS" provides operations with SMS by a GSM-modem connected as serial device. For now, there supported only sending SMS messages to a number of remote cell phone or GSM-modem. For sending there are supported: ECHO disable, PIN check and set, sending in PDU and the Text mode.
Output user protocol's XML-request structure
<cmd pin="1111" tel="+380XXXXXXXXX" text="{0|1}" err="1:Error">{SMSText}</cmd>
- cmd — command, for now only "send" allowed;
- pin — PIN-code to the SIM-card access;
- tel — telephone number of the receiver (remote cell phone or GSM-modem);
- text{0,1} — SMS in the text mode, only ASCII;
- SMSText — the message text;
- err — sets for the request result.
Configuring and using
- 1. Create an output transport of the type "Serial" and set its Identifier like to "SMS", one transport suitable for more receivers.
- 2. Set for proper address. The serial port speed, asynchronous data format and timeouts will adjusted by the function.
- 3. Create of need user protocol object based on the templates, with Identifier like to "SMS".
- 4. Place some requesting commands directly into presented or a new internal OpenSCADA-procedure like to:
req = SYS.XMLNode("send"); req.setAttr("ProtIt","SMS").setAttr("pin","1111").setAttr("tel","+380XXXXXXXXX").setText("Notify message");
SYS.Transport.Serial.out_SMS.messIO(req, "UserProtocol");
rez = req.attr("err").toInt() ? req.attr("err") : "OK";
- 5. RESULT: In the variable rez you will get "OK" if no errors occur and the message successfully transmitted to the receiver.
THE OUTPUT USER PROTOCOL PART "SMTP" provides operations with a SMTP-server for delivering EMails by their sending through TCP-Socket or SSL. For now, there are supported: TCP, SSL, AUTH, topic encoding for UTF-8.
Output user protocol's XML request structure
<send auth="{user}:{pass}" from="{FromAddr}" to="{ToAddr}" topic="{My Topic}" err="1:Error">{MessageText}</send>
- topic — topic of the message;
- from — sender address;
- to — destination address of the receiver;
- auth — authenticate user and password;
- MessageText — text of the message;
- err — sets for the request result.
Configuring and using
- 1. Create an output transport of the type "Sockets" or "SSL" and set its Identifier like to "SMTP", one transport suitable for more receivers.
- 2. Set-up for proper address, for Sockets(25) or SSL(465). The transport timeouts will be adjusted by the function.
- 3. Create of need user protocol object based on the templates, with Identifier like to "SMTP".
- 4. Place some requesting commands directly into allowed or a new internal OpenSCADA procedure like to:
req = SYS.XMLNode("send");
req.setAttr("ProtIt","SMTP").setAttr("from","noreply@oscada.org").setAttr("to","oscada@oscada.org").setAttr("topic","My topic").setText("My message");
SYS.Transport.Sockets.out_SMTP.messIO(req, "UserProtocol");
rez = req.attr("err").toInt() ? req.attr("err") : "OK";
- 5. RESULT: In the variable rez you will get "OK" if no errors occur and the message successfully transmitted to the receiver.
3.2 Control the remote initiative connections (initRemCntr) |
1.1 | GPLv2 | * | en, uk | Roman Savochenko |
The template of processing input initiative connections expands early one template initiative connections processing for the associated output transports by complete representing data of the remote OpenSCADA hosts on some aggregation server and with a possibility of control the remote hosts through the server, that is finishing the conception of data acquisition in the passive mode and the initiative connection.
The template does in whole:
- detecting a new connection from remote host, which has no ID;
- sending an acquaintance direct request to the established connection for getting KEY of the host, when it was already connected early, and for getting information about the host for creating ID of the host;
- setting ID for the connection;
- creating a record in the OpenSCADA hosts table for the connection and sending all followed requests already through the host;
- creating on the remote host a representative Logical Controller;
- creating on the remote host a representative DAQ.System Controller Object in the automatic mode, at missing any other there;
- processing the present DAQ.System Controller Objects to link the Logical Level parameters to them and creating some processing logical parameters, with updating for all sources at any reconnection;
- writing the generated key by a line "SrcKey: {KEY}" to description of the Logical Controller as a sign of finalizing the initialization;
- creating a Controller Object in DAQ.DAQGate with connection to the remote Logical Controller.
ID of the remote host is formed in the view "{HostDomain}{StatName}{RandKey}" and with limiting to 20 symbols, where:
- HostDomain — network host name-domain;
- StatName — station name of the OpenSCADA project;
- RandKey — random key in two HEX-digits.
Data model of the representative Logical Controller can contain both the generated links with processing parameters, and custom parameters, when the user is decided to publish some extra data. The generated items from DAQ.System are represents sources currently:
- "CPU", "MEM", "sensors", "Power", "uptime" => links in the "System (SYS)" container parameter;
- "fs", "hddstat", "hddsmart" => links in the "Disk (DISK)" container parameter with a processing one for "hddsmart" by the template base.DiskSMART;
- "netstat" => links in the "Network (NET)" container parameter;
- "ups" => links in the root with a processing one by the template base.UPS.
The aggregated data in DAQ.GAQGate can be lifted to up, or used in derivative DAQ objects, or whether directly on custom frames, or in future on a Dynamic Frame, which scheduled to implement; and without any additional action you will get notification about violations on the hosts.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| inTransport | Input transport | String | Input | Not attribute | Constant | Sockets.InitRemCntr |
| conTm | Connection time, ms | Integer | Input | Not attribute | Constant | 5000 |
| accessTm | Timeout of accessing, hours
Used for repeating to create representative objects of not accessed hosts and for removing old connections. |
Integer | Input | Not attribute | Constant | 24 |
| cntrUser | Access: user | String | Input | Not attribute | Constant | root |
| cntrPass | Access: password | String | Input | Not attribute | Constant | openscada |
| cntrObj | Control object in DAQ.LogicLev and DAQ.System | String | Input | Not attribute | Constant | RemCntr |
| prcTr | Processed connections | Text | Output | Read only | Variable | |
| this | Object | Object | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create an input transport of receiving the initiative connections of the module "Sockets" or "SSL" with the name like to "Sockets.InitRemCntr".
- 2. Set the previously created transport to the need address of opening the input socket and move it to the mode of creating the associative output transports, leaving the protocol field in empty.
- 3. For this template create and run a logical controller object or use any available with the required scheduling properties.
- 4. Create a logical parameter object and select this template for it. Enable the parameter.
- 5. In the tab "Template configuration" of the logical parameter object you need to set:
- Input transport — to value of the identifier of the input transport, created in the item 1, like to "Sockets.InitRemCntr";
- Connection time — timeout of connection to the initiative hosts after that to close the connection;
- Timeout of accessing — used for repeating to create representative objects of not accessed hosts and for removing old connections; zero or negative value for disabling the control;
- Access: user and password — user and password of the remote host with permition of creation there Logical Controller and DAQ.System Controller Object, that is the user must be included to the "DAQ" group;
- Control object in DAQ.LogicLev and DAQ.System — to ID of managed-created Controller Objects on the remote hosts.
- 6. RESULT: Starting the controller object (where this parameter was created) and when it was not started, we should get checking the specifying input transport for initiative connections and their initialisation in described above way and with notification processed connection in the attribute "Processed connections".
3.3 Initiative connections processing for the associated output transports (initConAssociateTrs) |
1.2 | GPLv2 | * | en, uk, ru | Roman Savochenko |
The template of processing input initiative connections was created to provide the last link of implementation and support for conception of data acquisition in the passive mode and the initiative connection, that is — the control of associative connections, created by the input transport at each connection.
After implementation this control together the new common-unified output transport connection function outAt() that template became deprecated for sources adapted to use the new mechanism, but you still can use the template for not adapted sources.
The function of creation associated output transports at connections is currently only supported by the module "Sockets" and for TCP-sockets.
- Total complexity: 0.9 HD[!]
- Sponsored by, for whole complexity: Elyor Turaboev, BLUE STAR GROUP Ltd
The control of associated transport means:
- obtaining a list of the associated transports, by the function assignTrsList() of the input transports;
- reading from new transports (opened) of identification information, which currently represents only the source object identifier;
- search, by the received identifier, the source object and assigning to it of this transport;
- registering in the attribute "prcTr" of the object type.
- checking of existing transports for their closure (detachment), for which performed the deregistration in the attribute "prcTr" of the object type and the establishment of the source object in the empty value; disconnected output associated transports are reused by the input one upon receiving a new connection then it is switched on.
The template can control the containers of data source objects, constructed both as DAQ-objects of the controllers and logical level parameters, what representing the data source and having a transport address definition field, and what generally defined by the configuration field "srcObjPath" of the format {CntrAddr}:{TrCntrFldAddr}, where:
- CntrAddr — container address, for example: "ModBus" — for DAQ-objects of the controllers, "LogicLev.CntrPLC" — for logical level parameters;
- TrCntrFldAddr — address of the transport control field in the source object, for example — "%2fcntr%2fcfg%2fADDR" for "ModBus"; what can be obtained in a configurator at the history of pointing on the control field in the status line.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| inTransport | Input transport | String | Input | Not attribute | Constant | InitiateCons |
| outTrTm | Output transport timeouts | String | Input | Not attribute | Constant | 10:0.1 |
| srcObjPath | Source object path | String | Input | Not attribute | Constant | ModBus:%2fcntr%2fcfg%2fADDR |
| prcTr | Processed transports | Object | Output | Read only | Variable | |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
Configuring and using
- 1. Create an input transport of receiving the initiative connections of the module "Sockets" with the name like to "InitiateCons".
- 2. Set the previously created transport to the need address of opening the input socket and move it to the mode of creating the associative output transports, leaving the protocol field in empty.
- 3. Provide a container of the data sources to which associative transports must be connected, which can be either a DAQ-module (such as "DAQ.ModBus"), or a logical controller (such as "DAQ.LogicLev.Sources"), or a parameter in it (such as "DAQ.LogicLev.PLC.Sources"), with logical level parameters representing the data source.
- 4. For this template create and run a logical controller object or use any available with the required scheduling properties.
- 5. Create a logical parameter object and select this template for it. Enable the parameter.
- 6. In the tab "Template configuration" of the logical parameter object you need to set:
- Input transport — to value of the identifier of the input transport, created in the item 1, like to "InitiateCons";
- Output transport timeouts — increase the first digit for very slow connections and typical is normal in most situations
- Source objects path — set according to the item 3, for the first part, and to the control field path, for the second part, for example, and typically for for "ModBus", is — "ModBus:%2fcntr%2fcfg%2fADDR".
- 6. RESULT: Starting the controller object (where this parameter was created) and when it was not started, we should get, in the attribute prcTr of the parameter for information about the processed and therefore successfully transport-linked data sources. In case of some violations, we will get the corresponding information in the attribute err of the parameter. The absence of a representative object for the received identifier is placed in the protocol of messages.
3.4 Weather (weather) |
1.0 | GPLv2 | * | en, uk | Roman Savochenko |
The template of acquiring weather data from different weather services in Internet and initially it is only Open Weather.
The weather data divided on current and forecast with their placing in corresponded objects, where current attributes placed directly in the root and forecast days (the "day" object) and times (the "time" object) inwardly corresponded day according to the current timezone. These data acquired at specified schedule independently for current and forecast, and by default the current ones are performed per hour when forecast ones per day. The data can be accessible by user both as directly and through a specially created widget of the main library.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| schedCur | Scheduling at CRON of current update | String | Input | Not attribute | Constant | 0 8-20 * * * |
| schedFC | Scheduling at CRON of forecast update | String | Input | Not attribute | Constant | 0 8 * * * |
| city | City ID | String | Input | Full access | Variable | 709932 |
| current | Current | Object | Input | Read only | Variable | |
| forecast | Forecast | Object | Input | Read only | Variable | |
| this | Parameter | Object | Input | Not attribute | Variable | 0 |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz | Real | Input | Not attribute | Variable | 1000 |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. For this template create and run a logical controller object or use any available with the required scheduling properties.
- 2. Create a logical parameter object and select this template for it. Enable the parameter.
- 3. In the tab "Template configuration" of the logical parameter object you need to set:
- Scheduling at CRON of current update — to value of need scheduling for current data acquiring in the CRON format, at empty the acquiring will be performed with period of execution the controller object;
- Scheduling at CRON of forecast update — to value of need scheduling for forecast data acquiring in the CRON format, at empty the acquiring will be performed with period of execution the controller object.
- 4. RESULT: Starting the controller object (where this parameter was created) and when it was not started, we should get the weather data in the attribute Current (current) and Forecast (forecast) and after setting your city code in the corresponded attribute. City code you can obtain from the official site in the URL after searching your city in the site form.
4 For WebUser
4.1 WebUser: HTTP File Server (fileServerHTTP) |
1.2 | GPLv2 | * | en, uk | Roman Savochenko |
The template for implementing a HTTP File Server directly in OpenSCADA, which is suitable one at missing a full-featured one for functions of servicing file requests from OpenSCADA Web-interfaces.
Currently there implemented only requesting files by the GET request of HTTP. There are supported also chunks and the Partial Content requests in single range and with forcing to this mode at some configured file size.
Template IOs
| Identifier | Name | Type | Mode | Attribute | Configuration | Value |
|---|---|---|---|---|---|---|
| rez | Result | String | Input | Not attribute | Variable | 200 OK |
| HTTPreq | HTTP request | String | Input | Not attribute | Variable | |
| url | URL | String | Input | Not attribute | Variable | |
| sender | Sender | String | Input | Not attribute | Variable | |
| page | WWW-page | String | Output | Not attribute | Variable | |
| HTTPvars | HTTP variables | Object | Output | Not attribute | Variable | |
| baseD | Base directory | String | Input | Not attribute | Constant | /data/share_res/local/Lib/ |
| fSzSolidLim | File size limit for solid reading, else enables the partial content | Real | Input | Not attribute | Constant | 10e6 |
| tr | Transport | Object | Output | Not attribute | Variable | |
| prt | Protocol | Object | Output | Not attribute | Variable | |
| f_start | Function start flag | Boolean | Input | Not attribute | Variable | 0 |
| f_frq | Frequency of calculation of the function, Hz Real | Input | Not attribute | Variable | 1000 | |
| f_stop | Function stop flag | Boolean | Input | Not attribute | Variable | 0 |
| f_err | Function error | String | Input | Not attribute | Variable | 0 |
Configuring and using
- 1. Create a page in the UI.WebUser module with some reasonable PageId.
- 2. In the tab "Procedure" you need to set:
- Base directory from which the page'll search files.
- File size limit for solid reading, else enables the partial content.
- 3. RESULT: Opening URL "http://{OpenSCADAHost}/WebUser/{PageId}/{MyFile}" in a WebBrowser will open and send you file on FS "{baseD}/{MyFile}".